With the three wire installation that you have now the neutral, equipment grounding conductors, the panel enclosure and the grounding electrode must all bond together.
Under the requirements of the 2008 code cycle three wire installations such as you have would be non-compliant. The 2008 cycle requires that an equipment grounding conductor be included with the feeders and the neutral be isolated at the remote panel board.