    Default Horizontal branch line fixtures

    We are working on a new modular home on a basement. There will be a horizontal branch line servicing the water closet, vanity, shower, & washer. All of the fixtures are individually vented. Does it matter where the water closet enters the branch line (i.e. upstream or downstream of other fixtures)?
    What about the washer?

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    Between the fixture and the wye fitting, there should be a vent.

    If the fixtures are vented that way, then the order makes no difference.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default toilets

    WHERE the fixtures go is immaterial. Whether you have the proper vents on them IS important regardless of how you have them arranged.