non ic rated recessed light

Users who are viewing this thread

quickfix

New Member
Messages
2
Reaction score
0
Points
0
Location
Pa.
I've installed 2 recessed lights (35 watt max.) in a closet ceiling, and didn't know about IC rating prior to installation. I've heard that you can add some kind of cover to shield the light from the insulation. Question....If I first placed a styrofoam cup over the can, and then covered that with a coffe can, would that be sufficient?

Thanks
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Most fixtures say something like "do not install in such a manner that will entrap heat"

If you box them in, make it a vented box.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Most of them also state something like "keep insulation and combustables a minimum of *** from the fixture". That is what you need to abide by. With some, you can build a big box around it, and put insulation over it...you need some minimum amount of air to disipate the heat. The alternative (and probably better solution) is to get one that is both air tight rated (AT) and insulation contact capable (IC) (you can get one without the other, but more common is probably both ratings together). Then, it won't leak air from your house into the ceiling and will still work while insulated, keeping your heat inside.

You can solder with a 15-watt soldering iron (not very big things though!)...it will get hot enough to melt metal, and ignite common building materials.
 
Last edited:

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
A styrofoam cup is not fire proof - so no
Usually 3" is the normal distance all the way around the can
Many people build boxes out of drywall

If too much heat builds up there is a thermal sensor & the light will shut off
 

quickfix

New Member
Messages
2
Reaction score
0
Points
0
Location
Pa.
Thanks Dave! Should the dry way box be vented? Can I use joint tape to enclose it?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Dig out the instructions that came with the thing, or find them on the web...each will be slightly different. Sometimes, they are listed ON the fixture. Follow them. If the volume and distance is okay, you might be able to seal it...the manufacturer tested it under certain circumstances to get a UL rating...you need to follow those conditions to make it safe.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
(B) Installation. Thermal insulation shall not be installed ABOVE a recessed luminaire or within 75 mm (3 in.) of the recessed luminaire's enclosure, wiring compartment, or ballast unless it is identified for contact with insulation, Type IC.

Box or no box insulation can no go over the fixture at all
 

Thassler

Member
Messages
106
Reaction score
1
Points
18
Location
Tennessee
I'm only a DIYr, but I've been through a house fire recently.

First - Calculate what it would cost to replace those two lights with IC rated units.

Second - Picture in your mind; Yourself and your family sifting through a pile of ashes that was once your home, looking for anything that can be salvaged.

Is the risk of loosing your house worth the cost of replacing with IC fixtures?

At some point in time someone is going to stick a 100w bulb in one of those fixtures because it was handy. Please, change them out for IC rated. Just my 2cents .....
 

Drick

In the Trades
Messages
460
Reaction score
19
Points
18
While we are on the subject - I installed 4 4" IC rated cans with 50W reflector flood bulbs in my bedroom. I'm not sure if the cans are air tight or not so I was considering enclosing them with sheet rock because I do have a moisture problem in my attic which I am trying to mitigate. However I noticed that the cans are very hot to the touch. Enough so that I removed the insulation from above the cans so that the heat can dissipate some.

Does anyone think that building a large-ish enclosure around the can would pose any risk? I would think not since they are rated IC but they do run quite hot.

-rick
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Flash point for wood is around 370-degrees. The lamp has a heat activated shutoff, not sure when it activates, but if you haven't noticed the lamp going off, you're probably okay. Build a box if you wish, won't hurt.
 

Thassler

Member
Messages
106
Reaction score
1
Points
18
Location
Tennessee
I boxed mine in using the scrap drywall we had leftover. It's called an "inverted soffit" - keep at least 3" of airspace around the fixture and seal the seams with tape or caulking. Insulate around and over it. There's a link somewhere, I'll try and find it.
 

Thassler

Member
Messages
106
Reaction score
1
Points
18
Location
Tennessee
<<Be sure to clear this method with the local building official. >>

Scuba_Dave is right - I ok'd it with my local inspector before I did it.
 