    I've installed 2 recessed lights (35 watt max.) in a closet ceiling, and didn't know about IC rating prior to installation. I've heard that you can add some kind of cover to shield the light from the insulation. Question....If I first placed a styrofoam cup over the can, and then covered that with a coffe can, would that be sufficient?

    Thanks

  2. #2

    Default

    Most fixtures say something like "do not install in such a manner that will entrap heat"

    If you box them in, make it a vented box.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Most of them also state something like "keep insulation and combustables a minimum of *** from the fixture". That is what you need to abide by. With some, you can build a big box around it, and put insulation over it...you need some minimum amount of air to disipate the heat. The alternative (and probably better solution) is to get one that is both air tight rated (AT) and insulation contact capable (IC) (you can get one without the other, but more common is probably both ratings together). Then, it won't leak air from your house into the ceiling and will still work while insulated, keeping your heat inside.

    You can solder with a 15-watt soldering iron (not very big things though!)...it will get hot enough to melt metal, and ignite common building materials.
    Last edited by jadnashua; 03-20-2009 at 11:44 AM.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    A styrofoam cup is not fire proof - so no
    Usually 3" is the normal distance all the way around the can
    Many people build boxes out of drywall

    If too much heat builds up there is a thermal sensor & the light will shut off
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  5. #5
    DIY Junior Member
    Join Date
    Mar 2009
    Location
    Pa.
    Posts
    2

    Default

    Thanks Dave! Should the dry way box be vented? Can I use joint tape to enclose it?

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Dig out the instructions that came with the thing, or find them on the web...each will be slightly different. Sometimes, they are listed ON the fixture. Follow them. If the volume and distance is okay, you might be able to seal it...the manufacturer tested it under certain circumstances to get a UL rating...you need to follow those conditions to make it safe.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    (B) Installation. Thermal insulation shall not be installed ABOVE a recessed luminaire or within 75 mm (3 in.) of the recessed luminaire's enclosure, wiring compartment, or ballast unless it is identified for contact with insulation, Type IC.

    Box or no box insulation can no go over the fixture at all

  8. #8
    DIY Senior Member thassler's Avatar
    Join Date
    Dec 2006
    Location
    Tennessee
    Posts
    106

    Default

    I'm only a DIYr, but I've been through a house fire recently.

    First - Calculate what it would cost to replace those two lights with IC rated units.

    Second - Picture in your mind; Yourself and your family sifting through a pile of ashes that was once your home, looking for anything that can be salvaged.

    Is the risk of loosing your house worth the cost of replacing with IC fixtures?

    At some point in time someone is going to stick a 100w bulb in one of those fixtures because it was handy. Please, change them out for IC rated. Just my 2cents .....

  9. #9

    Default

    While we are on the subject - I installed 4 4" IC rated cans with 50W reflector flood bulbs in my bedroom. I'm not sure if the cans are air tight or not so I was considering enclosing them with sheet rock because I do have a moisture problem in my attic which I am trying to mitigate. However I noticed that the cans are very hot to the touch. Enough so that I removed the insulation from above the cans so that the heat can dissipate some.

    Does anyone think that building a large-ish enclosure around the can would pose any risk? I would think not since they are rated IC but they do run quite hot.

    -rick

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Flash point for wood is around 370-degrees. The lamp has a heat activated shutoff, not sure when it activates, but if you haven't noticed the lamp going off, you're probably okay. Build a box if you wish, won't hurt.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11
    DIY Senior Member thassler's Avatar
    Join Date
    Dec 2006
    Location
    Tennessee
    Posts
    106

    Default

    I boxed mine in using the scrap drywall we had leftover. It's called an "inverted soffit" - keep at least 3" of airspace around the fixture and seal the seams with tape or caulking. Insulate around and over it. There's a link somewhere, I'll try and find it.

  12. #12

  13. #13
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    Be sure to clear this method with the local building official.
    Note the "disclaimer"
    Last edited by Scuba_Dave; 03-23-2009 at 08:35 PM.
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  14. #14

    Default

    Thanks for the link thassler!

    -rick

  15. #15
    DIY Senior Member thassler's Avatar
    Join Date
    Dec 2006
    Location
    Tennessee
    Posts
    106

    Default

    <<Be sure to clear this method with the local building official. >>

    Scuba_Dave is right - I ok'd it with my local inspector before I did it.