Thread: Venting below flood level

  1. #1

    Default Venting below flood level

    The upc code 905.3 states "Vents less than six inches above the flood level rim of the fixture shall be installed with approved drainage fittings, materials and grade to the drain."

    I am going to try to upload an image and was wondering if someone could tell me if the fiitting for the vent would have to be a wye and 8th bend on a shower trap arm.

    Any help appreciated
    Thank You
    Attached Images Attached Images  

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    If the vent is in the horizontal position, it would be a wye and 1/8 bend

  3. #3

    Default

    The vent would be horizontal or at a 45. Seems like lots of people cheat for lack of room and use a TY on its back.

    Thanks for reply