4 way switch

Users who are viewing this thread

eljefedavies

New Member
Messages
6
Reaction score
0
Points
0
Location
Nevada
I am trying to tie 2 lights together with 3 switches. The first light will have a 3 way switch near it, then a 4 way switch, then a 3 way switch and finally the second light. I know how to wire it by having both lights at the end of all the switches. However due to this being a remodel I am trying to minimize the running of wires. all lights and switches are currently in. 1 switch is controlling 1 light (the first 1 in the above question). The other light is being controlled by 2 3 way switches ( 1 will be changed to a 4 way (#2) and the last 1 will remain a 3 way (#3). Any help especially diagrams would be great. Thanks
 

Thassler

Member
Messages
106
Reaction score
1
Points
18
Location
Tennessee
The answer would depend upon where the power source starts (switch box or light fixture) and if onward unswitched power is needed and from where. Here's a link to several ways of wiring 4-way switched power:

(If linking to another site is not allowed, Moderator please remove.)
http://www.selfhelpandmore.com/switch-outlet/4-way/

You can also google "4-Way Switch Wiring Options"

**Not a pro - only a DIY
 
Last edited:

rgsgww

New Member
Messages
52
Reaction score
0
Points
0
Location
Ia
This is one way you could do it...It might not work in your situation....
 
Last edited:

rgsgww

New Member
Messages
52
Reaction score
0
Points
0
Location
Ia
You have a violation of Section 200.7(C)(2) of the NEC.
There will be a reinspection fee for this.

My understanding of section 200.7(C)(2) is that the white,gray, or marking of three continuous white stripes on a conductor, the conductor must be used for the supply, not the return.

Using it as the supply means that it must be permanently marked with paint or other means.

My image was wrong, so I deleted it.

This should be right?
 

Attachments

  • New Bitmap Image (4).JPG
    New Bitmap Image (4).JPG
    21.1 KB · Views: 525
Last edited:

eljefedavies

New Member
Messages
6
Reaction score
0
Points
0
Location
Nevada
This looks like it may work, a few questions though.

1. Why use the red wire then change to black? isn't the white one normally used then marked with black tape.

2. Where the 2 wire branches off the feed for the light, it looks like this is spliced in, can this be done? I would be able to do this in the 3 switch box, this would solve my problem. I am trying to avoid running a 2 wire from one light to the next due to ,locations and insulation etc...
 

rgsgww

New Member
Messages
52
Reaction score
0
Points
0
Location
Ia
This looks like it may work, a few questions though.

1. Why use the red wire then change to black? isn't the white one normally used then marked with black tape.

2. Where the 2 wire branches off the feed for the light, it looks like this is spliced in, can this be done? I would be able to do this in the 3 switch box, this would solve my problem. I am trying to avoid running a 2 wire from one light to the next due to ,locations and insulation etc...

You can use the red wire or black wire for the returning switched power, not the white. The white can only be marked and used as a supply conductor. As defined in 200.7(C)(2)

200.7(C)(2)

Where a cable assembly contains an insulated conductor for single pole, 3-way or 4-way switch loops and the conductor with white or gray insulation or a marking of three continuous white stripes is used for the supply to the switch but not as a return conductor from the switch to the switched outlet. **Or light** In these applications, the conductor with white or gray insulation or with three continuous white stripes shall be permanently re identified to indicate its use by painting or other effective means at its terminations and at each location where the conductor is visible and accessible.

You can splice two wires from the switch box, but you need to watch box fill.
What type of lights are these? cans can usually accept two romexes.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Maybe this will help

this one is from the panel or some other place like a rec. or another switch

fourwayswitchfromsource.jpg


This one is if the power is at the light

fourwayswitchfromlight.jpg


if you have any more questions I feel sure someone will answer but I have to go for now
 
Last edited by a moderator:

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
circuits

ALL light circuits have the switches at one end and the light at the other, regardless of how they are physically located. The two 3-ways could be next to each other and the 4-way at the other end of the house, but they would still have to be daisy chained together as if they were located right next to each other. You have to think about the way the switches have to be wired together, NOT where they are located relative to the light fixture.
 

eljefedavies

New Member
Messages
6
Reaction score
0
Points
0
Location
Nevada
Thanks for all the help. I have it all completed, I was just hoping to minimize the pulling of new wires, but it wasn't as hard as I anticipated.
 