    I find repairs straight forward it's the work to find what's causing the problem the hard part. I need a bit of confirmation here in my thinking process. I've got a pressure switch and therfore a pump cycling on and off every 30 secs. I turned off the valve coming from the well motor to the pressure tank. All lines from the pump to anything else is off so no water is flowing anywhere. The pump/pressure switch continues to cycle. I'm thinking the foot valve is leaking?

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Default

    What type of well/pump do you have?

  3. #3
    Porky Cutter,MGWC Porky's Avatar
    Join Date
    Jan 2008
    Location
    Virginia Beach, VA
    Posts
    727

    Default Do you have a pressure tank?

    All pumps (above ground or submersible) must have a pressure tank to work properly. Pumps without tanks will cycle!

  4. #4
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    Porky's right and another thing. There should not be a valve between the pump and tank. After the tank is fine.

    If the pump still cycles while that valve is open the tank is waterlogged.

    If the pump cycles every 30 seconds, is this with this wrongly placed valve on or off? Once the pump comes on, how long does it run before shutting off again?

    bob...

  5. #5

    Default pump cycling

    The pump is a submersable set down the well casing approx 100'. When I say valves I mean on/off valves not check valves. With all valves closed ie., with no water entering the pressure tank from the well, the pump still cycles. Cycle time is approx. 30 secs. Time is always consistant. I thought there was a foot valve located somewhere down the well casing just before the pump motor?

  6. #6

    Default Question

    Porky, just to confirm, the pump will cycle under 2 ways. 1) With all valves closed and no water allowed to go to the pressure tank. 2) I open all valves and the pressure tank is water logged. Is this correct?

  7. #7
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    There should never be a valve, or anything like a filter, between the submersible pump and the switch that controls it. So if you have one, don't shut it, and plan on preventing it to be shut accidentally.

    If you shut a valve off after the presure tank/switch...

    You have a leak between the pressure tank and the pump. Probably the internal check valve in the pump, or a hole in a fitting or leaking fitting. If not in the well, then from the well into the valve you say is preventing water into the pressure tank.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  8. #8
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Exclamation

    If you don't have a leak, closing any valve installed before the tank would be effectively dead-heading the pump, which in time will damage it.

    With no water running anywhere in the house, a properly operating pump will pump up to the cut-out pressure and stop. This pressure will be maintained indefinitely unless the water is leaking out somewhere. If you close the main shut-off in the house (which should always be installed downstream of the pressure tank) and the pressure still drops, the leak has to be between the shut-off valve and the pump. As Gary said, the leak might be in the well or between the well and the tank.

    I asked what type of well as only knowing that could I answer the question about the foot valve. A submersible pump does not use a foot valve.

  9. #9

    Default Pressure relief valve leaking

    Got the new pressure tank installed. Did the pressure tank test and it was wter logged. Everything working now except the pressure relief valve. Seems to be leaking. I removed it thinking maybe dirt build up but appears to be clean. I have a new pressure tank so I'm assuming the tanks pressure does not jive with thr relief valve?

  10. #10
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Default

    Are you sure it is a pressure relief valve?

    In my experience, the only pressure relief valve installed in a residential water system is the one on the water heater. There is no reason for an additional pressure relief valve.

  11. #11
    Previous member sammyhydro11's Avatar
    Join Date
    Dec 2006
    Location
    Massachusetts
    Posts
    709

    Default

    Submersible pump systems need a pressure relief valve because of the high pressures they are able to create. If your pressure relief valve is leaking, it could be defective, corroded, or your shut off pressure is too high.

    sammy

    www.tylerwellandpump.com

  12. #12

    Default Pressure relief valve leaking

    Thanks Sammy

    I agree valve or pressure setting. I'll turn down the pressure setting on the pressure valve assembly and see what happens.

  13. #13

    Default Terminology

    Sorry about that last post, I should have said I'll adjust the pressure on the pressure switch not assembly.

  14. #14
    Previous member sammyhydro11's Avatar
    Join Date
    Dec 2006
    Location
    Massachusetts
    Posts
    709

    Default

    Your switch settings should be either 30/50 or 40/60 but not any higher.

    sammy

    www.tylerwellandpump.com

  15. #15
    Previous member sammyhydro11's Avatar
    Join Date
    Dec 2006
    Location
    Massachusetts
    Posts
    709

    Default

    Any higher than 60 psi will put too much stress on the diaphragm. A 30/50 cycle will give you more storage but less pressure.

    sammy

    www.tylerwellandpump.com