Thread: Super High pressure, but pressure switch appears to work properly

Hybrid View

  1. #1

    Default Super High pressure, but pressure switch appears to work properly

    Hi All,

    Over the weekend, I noticed that our showers suddenly became very powerful. Water was leaking at the faucet in the kitchen and one sink faucet was actually harder to turn on because of the increased pressure.

    I went down to the well tank thinking it was the pressure switch (I replaced this about 5 years ago). The points on the switch were all open. I cut power to the pump and pressure remained (no leak in the system) until water was used. As pressure dropped below 40, points closed (still no power to system) as if trying to fill the tank. Pressure continued to drop with use of water to nearly nothing.

    I turned the power back on and the points remained closed until reading at 60- they opened as they should, but pressure continues to build in the system. I am afraid I am going to compromise my plumbing if I leave the pressure that high.

    The points are not stuck in either open or closed and can be manually operated but pressure continues to build even though points are completely open and I can see daylight between all of them.

    Ideas? Thanks for your help.

    Mark

  2. #2
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    If the points are open and the pressure switch and all other equipment is wired correctly, there is no way the pump can still be running. If you really think it's still running, get a volt meter on the outgoing side of the switch and see if you have 230 volts there. If you do, you definately have something wired wrong.

    Your definition defies what goes on in a normal system.

    bob...

  3. #3

    Default

    Quote Originally Posted by speedbump View Post
    If the points are open and the pressure switch and all other equipment is wired correctly, there is no way the pump can still be running. If you really think it's still running, get a volt meter on the outgoing side of the switch and see if you have 230 volts there. If you do, you definately have something wired wrong.

    Your definition defies what goes on in a normal system.

    bob...
    I think you're right but I can watch the pressure on the gauge increase. This has been working properly for 8 years. Suddenly- this. I am going to replace the pressure switch. Will let you know after I get done. Will I need to recharge (pressurize the tank) when I am done with the switch? I just removed it, got kinda wet, and am going to the store now.

    thanks for your help,.

  4. #4
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    I would check everything while your doing this. Check the tanks pressure while the system pressure is zero.

    Your gauge might be messed up, so get a new one of those too while your out shopping.

    bob...

  5. #5

    Default

    Ok, I changed out the pressure switch and put one on that had the presets at 40-60, turned back on the power and watched...

    The pressure slowly built back up and when my gauge reached 60, the points opened (as expected) BUT, the pressure kept building until I turned it off at 80+. This tells me a few things:

    A. Pressure gauge is not failing as it read correctly the 60psi when the points opened.

    B. Old and brand new pressure switches behaved identically- properly functioning would be my guess.

    C. There must be some short in the system or something that does not allow the starter to disengage? When I cut power, pressure stops building. When I re-engage power (points are all OPEN) pressure builds.

    D. I am confused.

    One thought- could the air bladder in the tank be bad? Is this something that would cause the pressure to build even after the pump is off?




    thanks again for your help.

    M
    Last edited by yergnov; 03-02-2009 at 11:06 AM.

  6. #6
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,134

    Default

    Someone posted a very similar complaint recently. The fix was to clean the rust out of the pipe going to the pressure switch.

    Put your voltmeter on the wires to the pump while the system cycles. Then there will be no doubt as to whether the pump is on or off.

    Assuming your water heater isn't about to explode, the pump is the only thing that could make pressures like you speak of.
    Last edited by cacher_chick; 03-02-2009 at 05:47 PM.