YES! Don't place it in the showerAnd ideally not within easy reach of the shower. This can be hard to accomplish sometimes.
Only if you are planning on dropping it in the sink.
(NEC 210.11C3) The 20 amp circuit can only serve both the lighting and receptacles as long as this circuit ONLY SERVES THE ONE BATHROOM. No need for the $$$ GFCI breaker, just use a GFI outlet.
(NEC 210.52D) "At least one receptacle outlet shall be installed in bathrooms within 3 feet of the outside edge of each basin." Your good.
-rick