  1. #1

    Default Sewage pump could cause big mess

    I am installing 3/4 hp sewage pump in a downstairs addition because the downstairs bath is lower than the city main. It is installed to code complete with 2" vertical check and all.

    I was getting ready to make the final hook-up to my main when it occured to me that if I ever had a plug somewhere down my mainline and effluent couldn't flow to the city main, it would continue to pump and probably come out of the upstairs shower first, then the toilet, etc.

    Any ideas save installing a back-flow check at every discharge point? There is a shower, a tub 3 lavs and two toilets upstairs.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default valves

    Doing that would create more problems than you could possibly, or would want to, deal with. It is a definite possibility, but there are no GOOD ways to prevent it, other than preventive maintainance of the sewer.