    Question Bathroom remodel DWV Venting

    OK, am in the process of beginning plumbing for a bathroom remodel. The bathroom is a 8x8 square. The toilet and shower are more or less next to each other. The plan is to drain the shower into the 3" toilet drain line using a short horizontal run and a reducing wye; I don't see any problem with that.

    There is a stub wall between. the shower and toilet. Can the shower and toilet vents rise about 6" above the drain line, meet under the floor, and tee into a 2" vertical vent pipe that will run up the stub wall? Hope this question is clear... thanks for any/all advice.

    best regards,

    dw

    Corvallis, Oregon
    Last edited by dw; 10-20-2004 at 11:16 PM.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,632

    Default vent

    The way a plumber would do it would be for the vent to come up behind the toilet. The shower would be piped into a 2" side inlet Wisconsin/Cottage tee, (or whatever it is called in your region), so that it also used the toilet vent. The lavatory, if it was close to the toilet on the other side would be connected to a sanitary tee in the toilet vent.

  3. #3
    Plumber Deb's Avatar
    Join Date
    Sep 2004
    Location
    Idaho
    Posts
    200

    Default Deb

    Venting is the toughest part of this job and it is VERY unusual if someone (not a plumber) can lay this out correctly. It can be tough even when it is drawn out.
    You will need to completely revise your plan. The toilet must be vented before you can wye in another fixture--you cannot connect another fixture to the line between a fixture's p-trap and its vent (called the trap arm).
    HJ has given you (IMHO) the best way to run a bathroom group when it is small and the fixtures are in close enough proxcimity to not exceed trap arm maximums. Having enough vertical space can sometimes be a problem, though. If space requires that you take a horizontal vent off below the flood rim of the fixture, there are more rules yet. You cannot connect the vents below the floor. Vents should rise vertically and not be connected to other vents until they are 6" above the flood rim level of the highest fixture.
    Deb
    The Pipewench

  4. #4

    Default more on DWV venting

    Thanks guys for the responses!

    Here's what we ended up doing, I hope it's correct:

    Starting at the toilet, Just past the closet bend, the 2" shower drain connects to the 3" toilet drain. The toilet is wet vented about 18 inches thru this shower drain, then up thru the lid and out the roof. The faucet is on the other side of the room and will join the vent above the cieling.

    Does this sound OK?

    cheers,

    dw

  5. #5

    Default more DWV

    Quote Originally Posted by dw
    Thanks guys for the responses!

    Here's what we ended up doing, I hope it's correct:

    Starting at the toilet, Just past the closet bend, the 2" shower drain connects to the 3" toilet drain. The toilet is wet vented about 18 inches thru this shower drain, then up thru the lid and out the roof. The faucet is on the other side of the room and will join the vent above the cieling.

    Does this sound OK?

    cheers,

    dw
    I should have mentioned: this was a tricky situation, as the 1/2 of the bathroom that has the toilet and shower is over a cantilever, with concrete slab about 18" below (therefore toilet drain could not go straight down, back wall less than ideal for vent, etc). On the other side of the room (not cantilevered) is the unfinished basement, where the plumbing can be more conventional. Anyhow, I'm still interested in comments about this... I know it's not ideal, but I believe that the wet-vent as i've described it is OK to do in this situation? It was definitely difficult, but most of the DWV is roughed in at this point and it's looking good, I think.

    Thanks again for the help,

    dw

  6. #6
    kathywhite
    Guest

    Default

    Starting at the toilet, Just past the closet bend, the 2" shower drain connects to the 3" toilet drain. The toilet is wet vented about 18 inches thru this shower drain, then up thru the lid and out the roof. The faucet is on the other side of the room and will join the vent above the cieling.. Well, I in the middle bathroom remodeling too but I am having bad time finding website that are related to this topic
    Last edited by Terry; 01-23-2007 at 10:00 AM.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •