    During a conversation with two (2) local, licensed residential electricians and one of the local electrical inspectors, on a job site the other day> Any new residential construction after Jan.01, 2009 requires that all 120v circuits within a bedroom be GFCI protected on either a 15 amp or 20 amp circuit, and all 120v circuits within any one bedroom may not be on one circuit. They stated that this was to bring Georgia up to par with the NEC. These electricians and the inspector say this is overkill. You're opinions? Thanks, David

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    A) There is NO 2009 NEC. It is the 2008 NEC.

    B) They are talking about AFCI, not GFIC protection.

    I have no idea where Geprgia is on this. Many locations around the country have adopted the 2008 NEC, but have placed amendments on the AFCI requirements.

    Only someone who knows the actual codes in your particular area will be able to tell you.


    Quote Originally Posted by Thurman View Post
    ..., and all 120v circuits within any one bedroom may not be on one circuit.
    I have no idea what this means.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    Georgia accepted it as of Jan 1st 2009 according to this
    But as said you need to find out if it was accepted in full

    http://www.childoutletsafety.org/fil...doptionMap.pdf

    Also Tamper proof required everywhere (pretty sure)
    Outside must be tamper proof, weather resistant & GFCI

    I think those are the changes - we've been on int since Jan 1st 2008
    I just returned $52+ of 20a PRO heavy duty outlets I can't use
    And they don't have any 20a PRO tamper proof
    Plus the price is double now
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  4. #4
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Default

    NEC 2009 AFCI

    210.12 Are-Fault Circuit-Interrupter Protection.
    (AFCI)
    (B) Dwelling Units: All 125-volt, single-phase,
    15- and 20- ampere branch circuits supplying
    outlets installed in dwelling unit family rooms,
    dining rooms, living rooms, parlors, libraries,
    dens, bedrooms, sunrooms, recreation rooms,
    closets, hallways, or similar rooms or areas
    shall be protected by a listed arc-fault circuit
    interrupter, combination-type, installed to
    provide protection of the branch circuit.


    NC addopted the 2008 NEC last year Mandatory Starting JULY 3 2008
    with some exceptions. This section was delayed until JAN 1 2009

  5. #5

    Default

    Maybe a little more info and clarification as to what this was all about: It is a State of Georgia Amendment to the 2008 NEC, and is about arc-fault and not GFCI. The link I found is very long but it falls under Georgia's Amendments: "210.12 Arc-Fault Circuit-Interrupter Protection." From what I found it still doesn't explain them talking about not having all duplex outlets in one bedroom on a single circuit, although having the outlets in one room divided up on different circuits is the way I was taught to wire a room so if one circuit fails, you have another for lighting, etc. It seems to be that with any new ruling or amendment to a ruling it takes time for interpretation. I'm still learning every day about something. Thanks, David

  6. #6
    Master Electrician Chrissimms's Avatar
    Join Date
    Oct 2008
    Location
    Cohutta GA
    Posts
    3

    Default

    Georgia has had arc fault breaker requirements in bedrooms only for several years now. As of 1/1/09 GA has adopted the tamper resistant receptacles in most counties.
    Chris

  7. #7
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    Ga currently has arc fault for bedrooms only until 1/1/10 then it reverts the arc fault section from the 08 code.
    Here is the amendments
    http://www.dca.state.ga.us/developme..._effective.pdf