Thread: Proper Venting for basement bath?

  1. #1

    Default Proper Venting for basement bath?

    1. I would like to know if this is the proper setup for the DWV in a basement bath I have.

    2. My second question is, are you allowed to vent out the sidewall of a house or do you always have to vent through the roof?

    I hope this picture explains it well enough. The main picture is looking down from above.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    EACH trap needs a vent. Now, all of those vent lines can be combined 6" above the flood plane of the highest item sharing the vent system. Inspectors often like 42" (nominal kitchen counter +6"), but it could be higher, depending on what's there.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    The main vent stack must vent to the roof. Ventiing out the side of the building is not allowed.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default vent

    Depending on the actual demensions There could be several better ways of doing it, but one revision would be to not have the toilet vent horizontal out of the back of the tee. Most inspectors would not accept that tee, I assume you are showing a tee, on its back either.

  5. #5
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Almost nothing would pass there, from the improper use of the sanitary tee, to the flat vent. This is why we get paid the big bucks.

  6. #6

    Default

    So is the problem specifically with the toilet setup? Or is there also an issue with the vent for the Shower? I don't see anything wrong with the setup for the sink, is that correct?

  7. #7
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    If you are allowed to go horizontal with the vents, then this may work.
    The wyes are rolled slightly up, and all fittings below grade are wyes, long 90's or 45's. The vented portion needs to be above the flow line of the waste line. This works in Seattle where the UPC plumbing code is in effect. What city are you buying the plumbing permit in?

    Notice that the wye to branch off for the shower is before the vent for the toilet.

    All of the vents need to go through the roof. Sometimes I've put them up the side of the house and penetrated through the roof with a flashing.
    Attached Images Attached Images  