    Default Concern about slope

    Hi all,

    Great forum. First time poster with an issue that has been worrying me for a few weeks. I'm installing a new 2nd floor bathroom and have been following the latest Michigan plumbing code. The issue is where the shower drain meets the tub drain I mistakenly drilled the next joist hole too high. Now the "T" there is perfectly level instead of sloping down by 1/4" per foot per code.

    Here is a side view of the "T" in question:
    Name:  Bathroom Project 088sm.JPG
Views: 171
Size:  95.9 KB

    Here is a perspective view of the junction:
    Name:  Bathroom Project 096sm.JPG
Views: 129
Size:  76.4 KB

    In order for me to resolve the issue I would need to drill a larger hole in the joist which will violate the structual code (no hole within 2" of edge and not to exceed 1/3 of the width of the joist).

    Question is do you think this will be a major issue (with clogging) in the future or am I worrying too much?

    Thanks in advance,

    Tim

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    You have also altered the height of the shower drain, making is an ilegal S trap.
    I see too where you have the tub draining past the shower, which will siphon the shower trap.
    Also, you have a santee on it's side. At the least it should have been a wye fitting.

    Is any of this vented?

    So much wrong, in so little space.
    Last edited by Terry; 02-08-2013 at 06:02 PM.

  3. #3
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

    Default

    Thanks for the reply. I guess I'm not sure how the height of the shower drain was altered as I used a complete "P" trap. Right after the "P" trap it slopes down to the T.

    I did not think about the siphoning issue - uggg

    As for venting yes there is one 1.5" vent in-between the shower and the tub. It is located 16" from this T and 16" from the tub drain.

  4. #4
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

    Default

    Here is a crude sketch of the setup. Seems I have the same siphon issue with the vanity...
    Attached Images Attached Images  
    Last edited by denikar; 02-10-2013 at 05:53 PM.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,428

    Default

    EACH trap needs its own vent...as drawn, only the tub is vented.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

    Default

    Quote Originally Posted by jadnashua View Post
    EACH trap needs its own vent...as drawn, only the tub is vented.
    Understood and will do. Thanks for the reply.

  7. #7
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

    Default

    Better?

    Name:  setup2.jpg
Views: 120
Size:  63.6 KB

  8. #8
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,428

    Default

    Better, but still not right! The vent line must come off the trap arm at or before it connects to the main line. The problem is, water rushing by the trap arm connection can suck the trap dry if there isn't a vent to prevent that. Just adding a vent doesn't work, it has to be in the right place as well.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  9. #9
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

    Default

    Quote Originally Posted by jadnashua View Post
    Better, but still not right! The vent line must come off the trap arm at or before it connects to the main line. The problem is, water rushing by the trap arm connection can suck the trap dry if there isn't a vent to prevent that. Just adding a vent doesn't work, it has to be in the right place as well.
    OK I get it now I think. Thanks for the reply. Since the location of this branch is under the shower I will need to go horizontal for about 2ft to get to a place where I can go vertical:

    Name:  setup3.jpg
Views: 118
Size:  64.1 KB
    Last edited by denikar; 02-09-2013 at 11:42 AM.

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,428

    Default

    Not sure that's going to cut it either, but you're closer. COuld you run the trap arm from the shower that way, vent it, then turn and pick up the main drain line along that back wall? Or run it at a 45 towards that corner, run the vent up before joining the main line? One of the pros should comment before you tear things up, as I've probably missed something.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Quote Originally Posted by denikar View Post
    I will need to go horizontal for about 2ft to get to a place where I can go vertical:
    The part in red cannot be horizontal at the position you show it. If the shower drain in green ever clogged up, that horizontal section of the vent could get clogged with no way of unclogging the vent.


    You cannot turn the vent horizontal until it is a certain height above the flood level rim of fixtures in that group. Someone else should chime in with specifics.
    Attached Images Attached Images  

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    quote; Right after the "P" trap it slopes down to the T.

    That is the problem, it cannot "slope down" using those 1/16 bend fittings until AFTER the vent connection and the vent connection cannot be "horizontal" until it is 6" above the spill level of the fixture. You also cannot use a sanitary tee in a horizontal line. The installation might be better if you had designed a better routing BEFORE you started drilling holes.
    Licensed residential and commercial plumber

  13. #13
    DIY Junior Member denikar's Avatar
    Join Date
    Feb 2013
    Location
    Canton, MI
    Posts
    13

    Default

    Quote Originally Posted by hj View Post
    The installation might be better if you had designed a better routing BEFORE you started drilling holes.
    Yes I realize I screwed up. But I want to fix it. The joists can be sistered rather easily as I've already sistered 4 of them to meet the tub loading requirements and to meet the ceramic tile maximum allowed bend requirements.

    Here is what I can do (from Jim's suggestion):
    Name:  vent idea3.jpg
Views: 90
Size:  27.8 KB

    Can a vent connect to a line at a 45 degree vertical angle as shown?

  14. #14
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,154

    Default

    The vent needs to be as vertical as possible, and in no case lower than 45 degrees.

Similar Threads

  1. Concern I have about Soiree
    By mcgillgirl in forum Toilet Forum discussions
    Replies: 4
    Last Post: 10-28-2007, 05:20 AM
  2. Holding Tank Concern
    By gmacpro in forum Pumps and Tanks Well Forum & Blog
    Replies: 15
    Last Post: 09-19-2007, 08:50 AM
  3. Fiberglass tub/shower concern
    By just bob65 in forum Shower & bathtub Forum & Blog
    Replies: 0
    Last Post: 08-12-2007, 06:40 AM
  4. To whom it may concern
    By GrumpyPlumber in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 23
    Last Post: 06-27-2007, 02:17 PM
  5. to whom it may concern....
    By ana in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 06-30-2006, 08:18 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •