Thread: water heater vent stack

  1. #1
    DIY Junior Member fozzy12's Avatar
    Join Date
    Jan 2008
    Location
    North of Detroit, MI
    Posts
    27

    Default water heater vent stack

    I'm running a standard water heater in my garage. It's a 75 gal Brad White with a 4" vent. Do I need to run double insulated vent piping? I temporarily put it in with standard 4 inch vent, through a roof flashing with a storm collar and a cap. I'm getting it inspected and rather going through having it fail, I'd rather change it sooner than later. I have ample clearance where it passes through the roof and also through the second floor flooring.
    I'm in Michigan if that helps.

    Thanks

    Eric

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    At every point, including the roof, you must have 6" clearance in all directions to any piece of wood or drywall or other combustible material.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,662

    Default vent

    Why would you even take a chance with single wall? Use double wall from the ceiling to the vent cap.

  4. #4
    DIY Junior Member fozzy12's Avatar
    Join Date
    Jan 2008
    Location
    North of Detroit, MI
    Posts
    27

    Default water heater vent stack

    HJ,
    It wasn't a question of taking a chance with single wall, I didn't know any better. I assumed since the heater had a normal 4 inch stack on top of it, that single wall would be acceptable, leaving enough clearance around the pipe. Since I have found out differently from the inspector who was kind enough to return my phone call, I will be changing it out to double wall tomorrow. It will be inspected, I just wanted it to pass on the first inspection.

    Eric

  5. #5
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    Quote Originally Posted by fozzy12 View Post
    HJ,
    It wasn't a question of taking a chance with single wall, I didn't know any better. I assumed since the heater had a normal 4 inch stack on top of it, that single wall would be acceptable, leaving enough clearance around the pipe. Since I have found out differently from the inspector who was kind enough to return my phone call, I will be changing it out to double wall tomorrow. It will be inspected, I just wanted it to pass on the first inspection.

    Eric
    It is awsome that you are having this inspected. I was just wondering did you install this heater on an 18" stand?

  6. #6
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    [QUOTE=SewerRatz;181814]It is awsome that you are having this inspected. I was just wondering did you install this heater on an 18" stand?[/QUOTE]

    And another wrench is sucessfully lobbed into the works.

  7. #7
    DIY Junior Member fozzy12's Avatar
    Join Date
    Jan 2008
    Location
    North of Detroit, MI
    Posts
    27

    Default water heater vent stack

    NH,
    Sorry to disappoint you on the wrench throwing, it is installed on an 18 inch pedestal!

    Eric

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,662

    Default heater

    It only needs to be on a stand if it is in the garage. If the city has accepted the latest National Gas Code, and the heater has an FVIR burner, it only has to be on the stand if a car could impact it.

  9. #9
    DIY Junior Member fozzy12's Avatar
    Join Date
    Jan 2008
    Location
    North of Detroit, MI
    Posts
    27

    Default water heater vent stack

    HJ
    The water heater is in a separate building but since it has garage doors on it, it needs to be on a pedestal. Here it also needs to be protected from impact. That means either 4 inch steel posts filled with concrete, or a wall. I chose the wall, I planned on it anyway. It is an older heater so it doesn't have the newer burner that can sit on the floor.

    Eric

  10. #10
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    [QUOTE=nhmaster;181817]
    Quote Originally Posted by SewerRatz View Post
    It is awsome that you are having this inspected. I was just wondering did you install this heater on an 18" stand?[/QUOTE]

    And another wrench is sucessfully lobbed into the works.
    You know me I love them there wrenches. It is what I do best.