A boiler system with a PRV requires an expansion tank on BOTh the inlet to the WH and one in the boiler circuit. If you only have one, and it is in the boiler circuit, it is isolated from the potable water system, and won't do anything for expansion when using hot water in the house. Add one to the potable water system, on the cold side of the WH.