Built in microwaves.

In some cases vent hoods require a dedicated circuit. I assume because so many people are switching them out to micro/vent combos.


My understanding on the microwave was that if built in it needed a seperate circuit, if not, then it could use the small appliance circuit. Hmmm....

Thanks for the idea on the fridge for being 1st, whomever said that. I think I'm going to have 3 dedicated circuits for my kitchen area. I will probably try to include the fridge and possibly the d/w on those. The fridge will be on a wall, with only two 24" wide countertops, so not much room for appliances, but that will hopefully meet code. The D/W will be in a walk-in pantry, so not many appliances will be in use there either.

My bath is on two circuits. 1(20amp) feeds all receptacles and a pair of wall sconces, the other(15amp) feeds the ceiling light and exhaust fan along with the main floor bedroo and hall lights.

I'll try to figure out the sump/furnace and laundry area.
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
Kitchen should have more than 3 circuits.

As someone else said, just run extra. Code is minimum.

I believe bath should have GFI on seperate circuit with nothing else, unless one circuit covers the entire bath ONLY. You could run to GFI's of seperate bathrooms, but only if that's the only thing on the circuit.
 

Master Brian

DIY Senior Member
Messages
368
Reaction score
0
Points
0
Location
Kansas
Kitchen should have more than 3 circuits.

As someone else said, just run extra. Code is minimum.

I believe bath should have GFI on seperate circuit with nothing else, unless one circuit covers the entire bath ONLY. You could run to GFI's of seperate bathrooms, but only if that's the only thing on the circuit.


Really? Why do you think it needs more than 3? Not saying 3 receptacles, I'm saying 3 circuits. Maybe I should add, this isn't a HUGE Modern Kitchen. The main area of the kitchen will have the fridge, a gas range and hopefully a vent for the stove. Vent is questionable because of lack of ceiling height above stove. Will figure that out when I tear out a sofit in ceiling. I'm also not sure about a garbage disposal in the main sink, because I have a marble apron sink and if I can't get a good answer as to whether it is safe to hang one, I won't. Yes, the occaisonaly appliance will be brought out, but not enough countertop space for much. I'm thinking 2 circuits for this room. One for each wall.

Then I have a current laundry area that is going to be converted to a small walk-in pantry. That is the 3rd circuit and will house the d/w, countertop microwave another sink, with disposal, and a few appliances. This isn't large enough to do lots of work in, so it won't have many appliances being run often in there. Maybe a toaster. I may add a 4th, depending upon the d/w I buy. Hmmm....

The bath is one circuit, with nothing else on that circuit. One GFCI controls all the receptacles in the bath. Again, not a huge bath and it is 20amp.
 

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
I run based on what could be or possible needs
We have a counter Microwave - 1100 watts
Toaster oven - 1500 watts
Toaster - 800 watts
Coffee maker - 1200 watts or more
Crock pot - 1000+ watts - we have 3 going during a get together
Pancake griddle - 1000+ watts
Can opener - 100 watts
Mixer - cakes, potatoes = 450 watts
Think of everything else that may be plugged in: TV, radio, laptop, popcorn maker, ice cream maker, blenders (550w),

You really don't need a gourmet kitchen, we had 3 blenders going one summer :D

Do you really want to risk someone plugging something into the same outlet as your fridge & kicking the breaker?

I figure the wiring could last 50 years or longer. So it's also about a future owners use. I only want to do electric once

I'm looking at 7 total + 1 more in the sunroom
I'll have 3 small appliance circuits
Fridge
Dishwasher
Lights are on another circuit
Microwave will have its own circuit - it will be in a cabinet
Sunroom - open to the kitchen, we could have a table out there with crockpots, coffee maker etc
 

Sjsmithjr

In the Trades
Messages
314
Reaction score
1
Points
16
Location
Knoxville, Tennessee
Really? Why do you think it needs more than 3? Not saying 3 receptacles, I'm saying 3 circuits. Maybe I should add, this isn't a HUGE Modern Kitchen.

My home is a 1948 Bungalow of less than 1000 square feet which I renovated three years ago. The kitchen measures 9x13 which includes small eat in bar. It might suprise you learn that I have three circuits for the countertops (including the bar), a lighting circuit, a dedicated circuit for the range hood (which came later), a dedicated circuit for the refrigerator, a dedicated cicruit for an electric range, and a dedicated circuit for the dishwasher. I do not have a garbage diposal, but we pulled the wire anyhow. We also pulled the wire for undercounter lights.

I suggest you start with the requirements (i.e. code), add what it is recommended (i.e. a exhausting range hood over a gas range, circuit for the refrigerator, etc.), and go ahead a pull the wire for upgrades like a disposal now and whatever you do pull your permits and talk to the AHJ as soon as possible.

"This doesn't look like the usual DIY job, nice work." is not a bad thing to hear from inspectors and appraisers. The added value, safety, and convienence are worth going the extra mile if you ask me.
 
Last edited:

Master Brian

DIY Senior Member
Messages
368
Reaction score
0
Points
0
Location
Kansas
You guys make some good points. I'll look into more circuits. I still have plenty of room to go in my panel. I'm not sure if it is a 30slot or 40slot panel, but I do have a subfeed in basement and in the garage and I only buy the double breakers, since all my empty slots take those.

Code will definately dictate what I do.....then I'll look at the appliances that would be used on each circuit and do some math!
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
My understanding on the microwave was that if built in it needed a seperate circuit, if not, then it could use the small appliance circuit. Hmmm....

Thanks for the idea on the fridge for being 1st, whomever said that. I think I'm going to have 3 dedicated circuits for my kitchen area. I will probably try to include the fridge and possibly the d/w on those. The fridge will be on a wall, with only two 24" wide countertops, so not much room for appliances, but that will hopefully meet code. The D/W will be in a walk-in pantry, so not many appliances will be in use there either.

My bath is on two circuits. 1(20amp) feeds all receptacles and a pair of wall sconces, the other(15amp) feeds the ceiling light and exhaust fan along with the main floor bedroo and hall lights.

I'll try to figure out the sump/furnace and laundry area.

Brian

In the original post you said;
I have been looking through the 2008 NEC and I am trying to do a floorplan layout. Thanks

If this is a true statement then all you need is the section number so you can see the verbiage of the code for yourself.
Look closely at 210.23(A)(1) and (2). You will see that the idea of
I will probably try to include the fridge and possibly the d/w on those.
might be a bad idea.
 

Sjsmithjr

In the Trades
Messages
314
Reaction score
1
Points
16
Location
Knoxville, Tennessee
Last time my hubby worked on the dishwasher, he unplugged it... is yours hardwired in?

Mine is, and according to the local inspector, it had to be for my particular installation. For a corded dishwasher, the requirement was that the receptacle be located in accessible location, which he interpreted as being under the kitchen sink. The cord could be no more 4 feet in length (which I think is a local requirement). Hence mine had to be hardwired.
 
Last edited:

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Mine is, and according to the local inspector, it had to be for my particular installation. For a corded dishwasher, the requirement was that the receptacle be located in accessible location, which he interpreted as being under the kitchen sink. The cord could be no more 4 feet in length (which I think is a local requirement). Hence mine had to be hardwired.


The cord can be longer than 4', it can ONLY be 3' to 4' from the actual plug to the plane of the rear of the appliance, so in other words, since the dishwasher is 24" deep, I could install a 6' cord and meet code.


422.16 Flexible Cords.
(2) Built-in Dishwashers and Trash Compactors
Built-in dishwashers and trash compactors shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer where all of the following conditions are met:

(1) The flexible cord shall be terminated with a grounding-type attachment plug.
Exception: A listed dishwasher or trash compactor distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to 4 ft) measured from the face of the attachment plug to the plane of the rear of the appliance.
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be located in the space occupied by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.
 
Last edited:

Sjsmithjr

In the Trades
Messages
314
Reaction score
1
Points
16
Location
Knoxville, Tennessee
Just goes to show there's the NEC and there's the local interpretation and amendments. The AHJ held me to 4 feet total length and the receptacle had to be under the sink.

I do appreciate the clarification as to current NEC requirements, however.

Thanks Chris.
 
Last edited:

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Just goes to show there's the NEC and there's the local interpretation and amendments. The AHJ held me to 4 feet total length and the receptacle had to be under the sink.

I do appreciate the clarification as to current NEC requirements, however.

Thanks Chris.

People make mistakes, nobody is perfect, but I do try to educate.... glad you learned something today. :)
 

RayP

Vocational Instructor
Messages
13
Reaction score
0
Points
0
Location
Syracuse NY
consider a feeder..

If I could redo my complete house rewire, I would use a feeder and put a panel near the kitchen. In fact, I will likely do this this summer. This feeder is a 240vac line, at least 10awg, better 8 awg. You can then run seperate ckts to each appliance, without having to pull the ckts all the way from the main service panel. 30A or 50A will never be used at the same time, so do some thinking on what you can expect to be the most appliances on at one time. Balance the load by putting the ckts strategically on both legs. So microwave on one leg, refrig on the other, as these two are most likely to be on at the same time.
 

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
That can depend on the kitchen & where the main panel is located
I don't like a panel in the kitchen anywhere near a sink (in the room)
Something about the wife having dripping wet hands & kicking out a breaker & going to turn it back on...or a child
My panel is only about 5' away under the kitchen
I could see this (sub panel) for a big kitchen
 

Master Brian

DIY Senior Member
Messages
368
Reaction score
0
Points
0
Location
Kansas
Luckily my panel is actually fairly close to the kitchen, about 6-8' down a half flight of stairs, so running wires will be easy.

IF my fridge and d/w are on the same circuit as other receptacles they won't be on the same circuit as each either.

Right now, the fridge is on the same circuit as the m/w, some basement receptacles and some bedroom receptacles. I even think it might be on the same circuit as the upstairs bath, but I haven't confirmed that. I just know the previous owner had told me if his wife ran the hairdryer and the microwave at the same time the breaker would trip..... Haven't had that, but I've also changed the panel from a tiny 60amp panel to a large 200amp panel.

The toaster and microwave DO trip the circuit....
 