Thread: Tankless in an unconditioned NJ attic

  1. #31
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Quote Originally Posted by Noth Jersey View Post
    I really wanted to colocate the heater with the water softener and the blasted flow restricting sediment filter, but they sit in the corner of the house with the main entry door, porch, windows on both walls, and sidewalks below (this is a largely above-grade walk-out basement). If I ran the vent along the rim joist, I'm not sure I could maintain clearance from combustible materials. The twenty-foot run would also require a five-inch drop for condensate drainage.

    So the whole freeze protection to -30 is inaccurate? The advice I got was post-purchase from the Rheem folks. They seemed pretty convinced that it would operate OK in the attic. Macplumb 777 told me about a freeze kit from Paloma, which apparently owns Rheem. I don't like the sound of having the coil freeze solid.
    *UPDATE*

    Well, the freeze kit thing is not available for any new models.

    At any rate, I just called Rheem again and they assured me that the water heater would survive -30 amibient temperatures. They said the only real concern is having a vent that is sufficiently long. They recommended a cold-weather vent kit with a damper-style end cap.

  2. #32
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Talking good luck.....

    Quote Originally Posted by Noth Jersey View Post
    *UPDATE*

    Well, the freeze kit thing is not available for any new models.

    At any rate, I just called Rheem again and they assured me that the water heater would survive -30 amibient temperatures. They said the only real concern is having a vent that is sufficiently long. They recommended a cold-weather vent kit with a damper-style end cap.

    I dont think I would trust anything that Rheem says.
    never trust a Techey that teaches theory.....


    yes, -30 that is pretty damn cold, but it dont take that to freeze pipes
    ....

    you had better be installing that unit with some sort of drain pan under it. Something Like a washing maching pan with a drain to the outside...

    ....just in case those Rheem techs are wrong....


    Also, I dont understand how the water lines going to and from this unit in that -30 temp area attic in New Jersey are supposed to keep from freezing and flooding your home either...


    are they telling you to run heat tape on all the lines
    all the way to the unit???


    and if the unit sits without comming on for a whole day
    in those harsh conditions, wont that coil get a little frosty??


    is their some sort of fail-safe on this ??

    Being installed the attic of your home,

    I would be very hesitant about this....


    .

  3. #33
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Quote Originally Posted by master plumber mark View Post
    I dont think I would trust anything that Rheem says.
    never trust a Techey that teaches theory.....


    yes, -30 that is pretty damn cold, but it dont take that to freeze pipes
    ....

    you had better be installing that unit with some sort of drain pan under it. Something Like a washing maching pan with a drain to the outside...

    ....just in case those Rheem techs are wrong....


    Also, I dont understand how the water lines going to and from this unit in that -30 temp area attic in New Jersey are supposed to keep from freezing and flooding your home either...


    are they telling you to run heat tape on all the lines
    all the way to the unit???


    and if the unit sits without comming on for a whole day
    in those harsh conditions, wont that coil get a little frosty??


    is their some sort of fail-safe on this ??

    Being installed the attic of your home,

    I would be very hesitant about this....


    .
    Yeah, the attic won't be hitting -30 here. -15 would be a record setting day. We don't go negative very often. The average low during the coldest part of the year is 14.

    At any rate, I'll be running the 1" pex underneath the insulation. The only exposed area will be the 18" portion up to the water heater. Maybe I'll just run the heat tape for the last few feet. I probably will put a drain pan under the unit. The problem with putting the unit in my basement is supplying air for combustion. 199k btus requires a little more volume than we have down there.

  4. #34
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Talking small hint....

    [quote=Noth Jersey;198641 The problem with putting the unit in my basement is supplying air for combustion. 199k btus requires a little more volume than we have down there.[/quote]

    if you can put it in your basement,
    that is where it would be wise to do it...

    getting combustion air to a applinace is as easy as
    just putting in a dryer vent hose to
    the outside....

    someday over the next decade it will certainly freeze
    up in the attic and its just a matter ot when..

  5. #35
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Quote Originally Posted by master plumber mark View Post
    if you can put it in your basement,
    that is where it would be wise to do it...

    getting combustion air to a applinace is as easy as
    just putting in a dryer vent hose to
    the outside....

    someday over the next decade it will certainly freeze
    up in the attic and its just a matter ot when..
    What do you think about extending the house envelope to the attic, i.e., removing insulation between the ceiling and building an enclosure around the heater? I would have to put in a fairly large louvered vent in the door. I guess I could always put in a couple of thermostatic outlets for heat tape and a space heater.
    Last edited by Noth Jersey; 04-29-2009 at 07:37 AM.

  6. #36
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    There are all sorts of fire code and structural issues with moving something like this into the attic and opening up the space. At least a tankless won't weigh as much as a tank would up there - most ceiling joists aren't designed for that kind of point load of a tank.

    Some of these things can be installed in small spaces like a closet...is there one near the master bath that could be usurpted for that use? You'd still have the makeup air problem, but that may be doable.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #37
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Quote Originally Posted by Noth Jersey View Post
    What do you think about extending the house envelope to the attic, i.e., removing insulation between the ceiling and building an enclosure around the heater? I would have to put in a fairly large louvered vent in the door. I guess I could always put in a couple of thermostatic outlets for heat tape and a space heater.
    A 200kbtu/h burner needs much more than a dryer hose for combustion air unless it a sealed-combustion setup. Backdrafting or lean operation due to wind-driven and exhaust fan pressure differentials are real possibilities (even in forced-draft models.) Good luck passing inspection if you're just plopping in a dryer hose into the space. (Good luck with getting it INSURED too.) 200kbtu/h is more burner than many/most home heating boilers or furnaces in NJ, and needs to be treated accordingly.

    Usually the freeze protection on these suckers relies on having reliable power. If an ice storm took down all the lines an you're out of power for a few days in winter (as happened to me this past December), if the unit is outside the thermal envelope of the building you're basically screwed. (Which DIDN'T happen to me. My HW heater lives in an insulated conditioned basement, it never got below 40F even on nights when it was 10F outside.)

    There are many good reasons (well beyond the scope of a hot water heater discussion) for converting attics into sealed, insulated-rafter conditioned or semi-conditioned space and dispensing with attic venting. It's both easier and better than you might think. A condensed encyclopedic overview of published research lives here:

    http://www.fsec.ucf.edu/en/publicati...CR-1496-05.pdf

    There are also very good reasons for going with sealed-combustion water heaters & boilers, especially if you have tightened up the place a lot (or plan to.) Takagi makes sealed-combustion kits for all of their hot water heaters, and other manufacturers have models/kits that are sealed combustion as well. Backdraft preventers on the venting offers quite a bit of freeze protection from wind (assuming it's inside the thermal envelope of the building) but can only be used on forced-draft models, (which would be most models over 100kbtu/h- I'm less familiar with Rheem, but I'd be surprised if it wasn't.)

  8. #38
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Default That sounds like a lot of WORK to me

    Quote Originally Posted by Noth Jersey View Post
    What do you think about extending the house envelope to the attic, i.e., removing insulation between the ceiling and building an enclosure around the heater? I would have to put in a fairly large louvered vent in the door. I guess I could always put in a couple of thermostatic outlets for heat tape and a space heater.

    the last time I re-did an attic, I sort of remember it being a lot of nasty , dirty , hot and
    god awful grimey work......

    and you are wanting to do all this just to get your tankless unit up there...


    basically you are going to increase the overall area of your home that needs to be heated , increaseing your yearly heating bill and cooling bill,
    I suppose that is a good thing if you ahve been wanting to do this anyway someday...


    but to go through all this work just to be able to
    save a few dollars a month with your tankless water heater...???


    Why not put it in the basement, and simply put in a large enough
    vent to the outside of the home for air>???



    anyway, enough on this topic,

    you do whatever makes you happy,

  9. #39
    DIY Member ChuckS's Avatar
    Join Date
    Mar 2009
    Location
    Aurora, CO
    Posts
    96

    Default

    Here is the heater I have. It is rated down to -30. It has a built in heater.

    http://www.tanklesswaterheaters.com/waiwelaph28ri.html

  10. #40
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default *update*

    The plumbing inspector said he'll probably want me to open up the attic to the conditioned portion of the house. I don't think he realized that my home will likely not provide sufficient combustion air for a 199k btu water heater. I could place the water in a basement utility room next to the water softener and the expansion tank, but boring a 5-1/2" hole for combustion would cause the same sort of freeze problem as putting the unit the attic, right?

    Is a buying a direct-vent unit my only practical option at this point?

  11. #41
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Talking boreing a-hole

    dryer vents are 4 inches round and no one complains about them....

    you want it to be faceing downwards towards the floor... no different than many closets with
    a pipe from the attic going down to the floor for air...


    A 50 power vent is probably a better choice...

    the bradfords are energy star rated too...

  12. #42
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    I'm afraid I'd need a 150 gallon tank heater for my 215 gallon bathtub. I'm not even sure a tank would fit in that closet. What type of vent material would you use to draw air from the attic? PVC? Flexible aluminum vent? Rain gutters? Since this closet sits in an exterior corner directly beneath the entryway to the house, I would have to run 7 pieces of 3" round duct up an exterior wall to provide sufficient air. What would be the consequences of notching my bottom plate to that degree?
    Last edited by Noth Jersey; 10-03-2009 at 10:51 AM. Reason: Math error

  13. #43
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Actually, I guess I would need 7 vents since it's a vertical duct, correct?

    Required free area of duct:
    199,000 btu/4000 btu/inē ≈ 50 inē

    Area of 3" duct cross-section:
    1.5ē*3.14 = 7.077 inē
    Last edited by Noth Jersey; 10-03-2009 at 10:42 AM. Reason: Math error

  14. #44
    DIY Junior Member ferd's Avatar
    Join Date
    Mar 2008
    Location
    Ohio
    Posts
    15

    Default

    Better check your math.

  15. #45
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Nice catch! Thanks.
    Last edited by Noth Jersey; 10-03-2009 at 10:42 AM.