    What if someone added additional light fixtures to that one fixture that's on 14 gauge wire? Would that pose a risk? In other words if they added 6 or 7 high hats to that fixture.
    Gabe

    Don't follow my advice, I only know a thing or two about a thing or two.

  2. #17
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,447

    Default

    As long as any wiring you add is adequate for the CB you have installed, you should be okay. To daisy-chain a bunch of lights, you wouldn't want to then switch to the small gauge wire they use internally - it must comply with the main circuit's requirements.