Thread: wire gauge change mid circuit

  1. #1
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default wire gauge change mid circuit

    Question,
    Am I allowed to change a 12 gauge circuit to a 14 gauge lighting circuit? I would expect the other way to be an absolute no no.

    Thanks in advance

  2. #2

    Default

    Only if the breaker was a 15A breaker.

    14awg = 15A
    12awg = 20A

    Why would you even consider that?
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  3. #3
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    Yes obviously. Just wanted to know if it would pass inspection if he saw 2 different gauges even though the breaker was still 15amp.

    TY

  4. #4
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    What do you want to do?
    Put a 15a breaker (1800 watts) on 12g wire
    --allowed, but as stated - why? breakers are the same $$

    You can hook up lighting to a 12g circuit (2400 watts)

    Do you want to run 14g wiring now to lights from a 12g circuit?
    I would never mix wiring in a circuit, not sure about code on that
    The problem is when someone looks at the wire in the breaker panel, sees 12g wire & upgrades the breaker to a 20a
    The 14g wire may be hidden & unknown
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  5. #5
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    Sorry,
    I didn't answer your question.

    Well the house was rewired with 200 amp before I bought it and I see 2 cases of it done. I guess it was cause the installer had extra 3wire in 14 that he used instead of getting more 12/3. Kind of cheap. I plan to replace it when I redo that room so if I evern need to change 20amp I will be set in the future.

    Thanks

  6. #6
    DIY Junior Member jamiedolan's Avatar
    Join Date
    Nov 2008
    Location
    Wisconsin
    Posts
    28

    Default

    Quote Originally Posted by rockycmt View Post
    Sorry,
    I didn't answer your question.

    Well the house was rewired with 200 amp before I bought it and I see 2 cases of it done. I guess it was cause the installer had extra 3wire in 14 that he used instead of getting more 12/3. Kind of cheap. I plan to replace it when I redo that room so if I evern need to change 20amp I will be set in the future.

    Thanks
    I would ensure the 12 awg in your panel is clearly labeled "warning connected to 14awg wire, must be protected by 15A breaker"

    Yes, I have seen this done, and I don't know why they did it either. It is wrong. You can have a smaller gage wire connected to the 12gage and maintain 20A protection, but only if that smaller gage wire feeds (and is attached to by the manfacture) a UL approved fixture (i.e. hanging lamp with 16 gage cord)

    What do you mean it was because he had an extra 3rd wire in the 14? When I hear things like that, I think MWBC, use due caution.

    Jamie

  7. #7
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    I feel the installer used 14/3 (Cause he had it on hand) to wire a ceiling fan instead of purchasing more 12/3 to keep the gauges the same. He cheaped out.

  8. #8
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    I doubt The installer was an elictrician....most likely a H/O not knowing any better.

  9. #9
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Scuba_Dave View Post
    The problem is when someone looks at the wire in the breaker panel, sees 12g wire & upgrades the breaker to a 20a
    The 14g wire may be hidden & unknown
    I donít know of a qualified electrician that would automatically up grade a 15 amp overcurrent device to a 20 amp no matter what size wire it was installed on.
    This type of question is one of those thousand question that the average Do-It-Yourselfer wouldnít ask about that could end up getting someone hurt.

    Quote Originally Posted by rockycmt View Post
    Well the house was rewired with 200 amp before I bought it and I see 2 cases of it done. I guess it was cause the installer had extra 3wire in 14 that he used instead of getting more 12/3. Kind of cheap.
    Quote Originally Posted by rockycmt View Post
    I feel the installer used 14/3 (Cause he had it on hand) to wire a ceiling fan instead of purchasing more 12/3 to keep the gauges the same. He cheaped out.
    Twice you have said that the installer did something that was cheap. I often will leave a panel with #10 and later change over to #12 and install a twenty amp breaker. This is something done every day where the well is a long way from the house.
    I have also left the panel with #12 and changed over to #14 where there was a long pull such as on the second floor of a house with the panel on the outside wall of a two car garage. This #12 being protected by a 15 amp breaker was installed for the same reason as the #10 to the well, voltage drop.


    Quote Originally Posted by jamiedolan View Post
    I would ensure the 12 awg in your panel is clearly labeled "warning connected to 14awg wire, must be protected by 15A breaker"
    First lesson is that it is the overcurrent device that determines the amperage of the circuit not the wire. There is no need to label anything as everyone should know that you never replace an overcurrent device with a lager one no matter what size wire is installed. This in itself is a big NO, NO!

  10. #10
    Extreme DIY Homeowner Scuba_Dave's Avatar
    Join Date
    Jan 2009
    Location
    South of Boston, MA
    Posts
    885

    Default

    If a homeowner asked an electrician to upgrade a 15a breaker in the box connected to 12g wire an electrician wouldn't do it? I highly doubt that. I've had people post that their electrician didn't even run GFCI for an outside outlet
    I never downgrade wire in a run (12g or 14g), just asking for trouble down the road. I can see doing it with #10 for a long run to a pump
    And if the lower gauge wire is hidden, how is anyone to know its there?

    The majority of breakers in my old panel were 15a breakers. Wire was too old to properly judge the gauge, one circuit was 2 wire only, no ground. About 90% of my house has been rewired & brought up to code

    I would never replace a breaker without verifying what was connected & the wiring run. But again if the lower gauge wire is hidden in the wall your kinda screwed. But I doubt most homeowners would think that someone "went cheap" & used mixed wire in a run. Most know nothing about voltage drop. They see 12g wire, that can handle 20a

    The problem always is, not necessarily what is wired/ completed know - but what might be changed years down the road by a new owner or another electrician
    DIY Handyman (not 4 hire)
    I have enough to do to my own house

  11. #11
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by Scuba_Dave View Post

    The problem always is, not necessarily what is wired/ completed know - but what might be changed years down the road by a new owner or another electrician
    Not my problem, if you dont know what your doing then dont do it...

  12. #12
    In the Trades maintenanceguy's Avatar
    Join Date
    Aug 2008
    Location
    Pennsylvania
    Posts
    107

    Default

    It seems a little odd but not wrong.

    Wouldn't raise any red flags for me. As long as the CB is sized to protect the smaller wire size, no problem. Feel free to run 4/0 bugged to 14g as long as it's got a 15A breaker.

  13. #13
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Scuba_Dave View Post
    If a homeowner asked an electrician to upgrade a 15a breaker in the box connected to 12g wire an electrician wouldn't do it? I highly doubt that.
    An experienced electrician would not change a lower amperage with a higher amperage overcurrent device.
    Now maybe an inexperienced Do-It-Yourself Idiot might.
    Rule 1- Never change an overcurrent device for a lager one.

    Quote Originally Posted by Scuba_Dave View Post
    I've had people post that their electrician didn't even run GFCI for an outside outlet
    Remember that at one time they wasnít required to install them. Then again just because someone calls theirself an electrician does not mean that they are one

    Quote Originally Posted by Scuba_Dave View Post
    I never downgrade wire in a run (12g or 14g), just asking for trouble down the road.
    This is a choice that you make but I can promise you that someone who is making installations for a living will do so simply because it is called making a profit.
    Quote Originally Posted by Scuba_Dave View Post
    I can see doing it with #10 for a long run to a pump
    So why would it be alright for one installation and not for another?
    Quote Originally Posted by Scuba_Dave View Post
    And if the lower gauge wire is hidden, how is anyone to know its there?
    Ever thought about looking at the breaker size. This will give it away each and every time

    Quote Originally Posted by Scuba_Dave View Post
    The majority of breakers in my old panel were 15a breakers. Wire was too old to properly judge the gauge, one circuit was 2 wire only, no ground. About 90% of my house has been rewired & brought up to code
    Why would you need to judge the gauge of the wire when you have a perfectly clear 15 amp overcurrent device telling what the amperage of the circuit is?

    Quote Originally Posted by Scuba_Dave View Post
    I would never replace a breaker without verifying what was connected & the wiring run. But again if the lower gauge wire is hidden in the wall your kinda screwed. But I doubt most homeowners would think that someone "went cheap" & used mixed wire in a run. Most know nothing about voltage drop. They see 12g wire, that can handle 20a
    Without knowing you are making the perfect argument for not allowing the Do-It-Yourselfer to enter the realm of electrical work. You are saying in a very loud voice that you donít understand electrical installations.

    Quote Originally Posted by Scuba_Dave View Post
    The problem always is, not necessarily what is wired/ completed know - but what might be changed years down the road by a new owner or another electrician
    Again Never change out an overcurrent device for a larger one. This is the mark of ignorance. If one is going to just go around changing out overcurrent devices for larger ones why not just go all the way and do away with the darn thing completely. Shucks, it had a #12 so it must be good for at least 50 amps so lets just change it out, Silly, Silly, Silly.

  14. #14
    Remodel Contractor GabeS's Avatar
    Join Date
    Jan 2007
    Location
    Brooklyn NY
    Posts
    294

    Default

    You can have a smaller gage wire connected to the 12gage and maintain 20A protection, but only if that smaller gage wire feeds (and is attached to by the manfacture) a UL approved fixture (i.e. hanging lamp with 16 gage cord)

    Is this really allowed? There's no danger of overheating?
    Gabe

    Don't follow my advice, I only know a thing or two about a thing or two.

  15. #15
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    It's the same idea of plugging in a lamp...the circuit is still protected at the CB and main wiring...the key is that the thing plugged in is adequate for its INDIVIDUAL load as an assembly. A table lamp certainly is unlikely to have 12G wire (more like 18g or even smaller depending on wattage), but will work and be fine on this higher current circuit. Same is true with wired in items - their individual internal wiring doesn't need to comply but they do have to pass tests verifying safe operation. I know for certain that my a/c compressor's internal wires are at least a couple gauges smaller than the required wiring up to it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014