Toilet flange above or level with floor

Users who are viewing this thread

dmaceld

New Member
Messages
11
Reaction score
0
Points
1
Location
Idaho
I find several comments in this forum where the authors say a toilet flange should be on top of the finished floor. There are also a couple of posts where in that case the poster had problems with rocking toilets due to insufficient space between the flange and toilet bottom. I have a copy of Code Check Complete which is a summary of four primary building codes. In there the authors have an illustration specifically showing the flange top level with the finished floor as being the correct installation and a big NO circle over the illustrations showing the flange on top of the finished floor and below the finished floor.

What I find of the plumbing codes the only code requirement is for the flange to securely fastened to surface below it.

Soooooo, what is the correct positioning of the flange to avoid clearance problems and still have a water tight seal?
 
Last edited:

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
Only part in Illinois plumbing code is as follows.

Section 890.360 Water Closet and Pedestal Urinal

Fixture connections between drainage pipes and water closets, floor outlet service sinks and pedestal urinals, and earthenware trap standards shall be made by means of brass, copper, hard lead, plastic, or iron flanges; caulked, soldered, screwed or solvent welded to the drainage pipe. Flanges of hard lead, plastic and iron flanges for no-hub or compression joints shall be secured to the floor. The connection shall be bolted, with a gasket, washer or setting compound, between the earthenware and the flange. The floor flange shall be set on an approved firm base. The use of putty or non-drying plumber's putty manufactured specifically for plumbing installation is acceptable​

It does say it needs to be set on an approved firm base. I always put it on the sub-floor, and let the tile guys tile around it. So I make sure it will be installed flush with the finished floor.

 
Last edited by a moderator:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
There are two issues...the flange must be firmly attached, and, it is designed to sit OVER the finished floor and anchor through it. If the flange is installed tight to the floor surface AND that surface is flat and level AND the flange is not poorly designed AND the toilet is standard with decent quality control, you should be able to use a standard wax ring and get a reliable, waterproof, gasproof seal. A thick wax ring filling a wide space isn't as reliable (but could last a very long time if not disturbed) as a thinner one. Since a typical flange ring is only in the order of approximately 1/4" or so, if it was ultimately level with the finished floor, would having the wax an extra 1/4" be a major factor? Maybe if you got really aggressive with a plunger, but probably not.

Issues with a toilet not fitting are usually related to a flange that is not sitting ON the finished floor and is sitting above it, or not level with the floor. Also, some people think the use of a horn embedded in the wax ring is a good idea...the higher the flange is, especially on a 3" drain pipe, the more problems you'll have since that horn does have some uncompressable thickness and width and may not fit into the throat of the flange.

Essentially, any properly made toilet should fit on any code approved flange IF the flange is installed on TOP of the finished floor properly. There are a lot of junk toilets out there that may not meet industry standards.
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Always on the finished floor for proper tolerances between toilet and flange so the wax ring can do it's job to the best of its ability.
 

McMike

Plumber
Messages
10
Reaction score
0
Points
0
Location
Aurora IL
The last company I worked for(service plumbing and remodels) had a policy of flange on finished floor, the majority of the leaky toilet floor seals we were called to repair were 3inch PVC flange 10-15 years old, below floor level, if we used thicker wax we would still have problems within our 2 year warranty, so the company requires flange to be cut out and repiped to sit on FF, those flanges that were reset on FF would easily last well past our 2 year warranty, it was very rare to see a leaky floor seal with a flange set on FF
 

Donn2390

Member
Messages
67
Reaction score
0
Points
6
Location
Riverside, California
Now you have me worried...! I'm just in the process of installing a couple of Aquia lll. I have the old toilet removed and the flange cleaned up and ready to install.
Came back here to double check everything before dragging out the drill, and I see these comments on the flange being flush with the FF.
My flange is flush with the concrete floor, and the thickness of the tile below FF, maybe a quarter of an inch, but solidly mounted.
The old wax ring came off easily in one piece. It is about an inch and a quarter thick in it's compressed state. I'm guessing the existing wax rings must be the thicker ones.
The house is five or six years old and never had a leakage problem.
I'm heading for HD now to buy a couple of new wax rings and new water inlet pipes and some carbide drills..
I sure don't want to tear up my floor to raise the flange a quarter inch, so I'm going with the thicker ring and hoping all will work out, since it has worked for five years with the flange lower than FF.
The old closet bolts mounted in the flange are solid and appear to be like new. Is there any reason to replace them..?
Hopefully my wife will still be talking to me by the end of the day......??
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The wax must compress when you set the toilet...you need enough thickness to have that happen. There are flange extenders you can use rather than replace a flange.

Because of the way the toilet is designed, it might not leak unless there is an obstruction and the drain backs up. It could leak sewer gasses, though. Depends on your system whether you'd notice.
 

Donn2390

Member
Messages
67
Reaction score
0
Points
6
Location
Riverside, California
Thanks, Jim. I'm getting smarter by the minute. Fortunately HD is only a couple of blocks away.
I mentioned my old seal was an inch and a quarter. On closer inspection, it's two put together....!
I'm on the way back to HD to exchange a few parts, so I will check out a flange extention.
The good news is, the second toilet should be a breeze. This one has taken much longer than expected, but I prefer to go slowly and not screw anything up. If I had to depend on my plumbing abilities to put food on the table, I'd have starved to death long ago....
Good thing we have four bathrooms, or I might have to buy some rubber bands...! Looks like tomorrow before this one is working....
 

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
In the older days, when lead bends , and eventually copper drains were introduced, the codes expected you to affix the floor flange on top of the finished floor. The thickness of the flange played a big part in that thought process. It would allow all tolerances.

When plastic came into play (PVC and ABS) you will notice that the flange is slightly thicker. To compansate, they amended any codes to allow for the difference in thickness. We, in Canada, place our platic flanges flush with the finished surface (level with the tile floor) and or 1/8" higher than the finished surface. This would allow you to use a sponge gasket if you wanted to. (in both cases, always fastening the flange to the floor or subfloor)

Placing the PVC OR ABS flange on top of you finished surface, you are almost obligated to use a wax gasket, whether you like them or not. The wax will squeeze much further than your sponge gaskets and the flanges do not need to be exactly level. The wax will form to its new level, or lack of level
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
I have always understood the flange was to be set on top of the finished floor and will continue to do that on any flanges I install in the future. However, if I am asked to install a toilet and find a perfectly good flange installed flush with the floor, I will not hesitate to install the toilet. Now recessed another 1/4" is another matter, but that's for another thread.
 

Donn2390

Member
Messages
67
Reaction score
0
Points
6
Location
Riverside, California
Success...

Thanks to all for the good tips. One is installed with one to go. It turned out to be a slam dunk. With the exception of drilling four holes through tile and concrete, it was much easier to install than a standard toilet..!
Everything went smoothly, and it works perfectly with no leaks. I spent more time worrying and studying than installing. The next one will go quickly...
The flange being 1/4" below FF was simple to resolve. Fluidmaster makes a thicker wax ring, which handled the problem easily.
One benefit of having the socket adaptor is, you put it in place w/o the seal, and you can see and feel how much gap you have to deal with, and after it's installed with the wax ring, you can see and feel the results, so there is no guessing.
So far we love it, and I'm very happy I took Terry's advice and spent the extra hundred for the ADA....
 

dmaceld

New Member
Messages
11
Reaction score
0
Points
1
Location
Idaho
In the older days, when lead bends , and eventually copper drains were introduced, the codes expected you to affix the floor flange on top of the finished floor. The thickness of the flange played a big part in that thought process. It would allow all tolerances.

When plastic came into play (PVC and ABS) you will notice that the flange is slightly thicker. To compansate, they amended any codes to allow for the difference in thickness. We, in Canada, place our platic flanges flush with the finished surface (level with the tile floor) and or 1/8" higher than the finished surface. This would allow you to use a sponge gasket if you wanted to. (in both cases, always fastening the flange to the floor or subfloor)

Placing the PVC OR ABS flange on top of you finished surface, you are almost obligated to use a wax gasket, whether you like them or not. The wax will squeeze much further than your sponge gaskets and the flanges do not need to be exactly level. The wax will form to its new level, or lack of level

Well, it's been a few months and the bathrooms are done, along with all the house, and we are moved in! My experience with the toilet installations was pretty much dead on with the response above. I put the ABS flanges on top of, and tight to, the finished floor. I installed Toto Drake ADA elongated toilets, a favorite of this forum's followers. It turns out there isn't enough depth around the outlet to allow the use of some no-wax seals. The flange on the Fluidmaster seal I had was too thick and the toilet missed touching the floor by about 1/8". I used a no-wax seal I got from a plumbing supply house, don't recall the brand, that barely fit. In fact there still is a slight gap but the toilet doesn't rock. If I ever install another toilet I believe I will go flush, or maybe 1/8" above the finished floor. That should allow the use on any good seal, wax or no-wax.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
flange

quote; I have a copy of Code Check Complete which is a summary of four primary building codes. In there the authors have an illustration specifically showing the flange top level with the finished floor as being the correct installation and a big NO circle over the illustrations showing the flange on top of the finished floor and below the finished floor.

I always install it on top of the floor. If you have a toilet with a deep recess and the flange is flush with the floor, a conventional wax ring will not have any compression. The only way a flange on top of the floor COULD cause a wiggling problem would be if the toilet has a very shallow recess, and only the most mediocre toilets would have that, AND the flange is a plastic one with a very thick flange. Normally, the ONLY way to be sure the toilet is sealing properly is to have the flange on top of the floor.
 

dmaceld

New Member
Messages
11
Reaction score
0
Points
1
Location
Idaho
The only way a flange on top of the floor COULD cause a wiggling problem would be if the toilet has a very shallow recess, and only the most mediocre toilets would have that, AND the flange is a plastic one with a very thick flange.

The Toto Drake is a mediocre toilet???? The flange is an ordinary Nibco or Mueller ABS flange. The seal is a Fernco wax free. All stuff one could expect to work together nicely, but doesn't.
 

Rich B

DIY Senior Member
Messages
285
Reaction score
1
Points
16
Location
New Jersey
quote; I have a copy of Code Check Complete which is a summary of four primary building codes. In there the authors have an illustration specifically showing the flange top level with the finished floor as being the correct installation and a big NO circle over the illustrations showing the flange on top of the finished floor and below the finished floor.

I always install it on top of the floor. If you have a toilet with a deep recess and the flange is flush with the floor, a conventional wax ring will not have any compression. The only way a flange on top of the floor COULD cause a wiggling problem would be if the toilet has a very shallow recess, and only the most mediocre toilets would have that, AND the flange is a plastic one with a very thick flange. Normally, the ONLY way to be sure the toilet is sealing properly is to have the flange on top of the floor.

So HJ, this means you are installing toilet flanges against code guidelines ? I have read countless posts by you and other regular pros and everyone always says you must follow the code used in your area......I have that exact same Code Check publication mentioned above and it does say that toilet flanges must be flush with the finished floor.....Does the Code in your area say you can install a toilet flange above the finished floor?
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
code check

That "code check" book was written by someone using his opinions, it is NOT a plumbing code. There are "milllions" of flanges installed ON TOP of the flooring. The only ones even with the flooring are those in remodels or when the flange was preinstalled. It is NOT against code to put it on top of the floor, although it might go against the writer of the code check book, but I have never consulted him and do not know what his qualifications, if any, are.
 

Kordts

In the Trades
Messages
547
Reaction score
1
Points
0
Location
exurban Chicago
I just made some nice money because the installing mope plumber installed the flanges level with the finished floor. One leaked, causing the subfloor to get wet and mushy. I ended up using spacers to get the flanges where they belong, on top of the finished floor. I have never seen a flange on top of the finished floor leak yet, or cause the toilet not to set flush.
 