Originally Posted by
Gary Slusser
This aerator is fed from the well pump and holds water at atmospheric pressure right; meaning the aerator is not pressurized? Your shut off valve and then this check valve is on the outlet of the aerator tank right?
1. yes
2. yes the valves are on the outlet side
If so, you have flooded suction to the jet pump and the water level in the aerator tank is probably higher than the jet pump, right?
I believe that the water level in the aerator and the inlet to the jet pump are pretty close to equal, I'll have to check to be sure. I brought the outlet pipe up, then horizontal through the tank then back down about 6" on the outside of the tank to get it in line with the inlet on the jet pump, then horizontal to the the jet pump. I flooded the aerator when I primed the pump to force the air trapped above the normal water level out of the jet pump's vent; because this u-shape is above the aerator's water level and jet pump's inlet.
At the lowest water level in the aerator, if the pump inlet pipe is still lower your'e fine, if the water level is lower than the pump's inlet pipe, you need a foot valve in the aeartor on the end of the pump's suction line.
??????I have the outlet pipe/suction line to my jet pump terminate about 8" above the bottom of the aerator. This is my suction line. If I understand correctly you recommend a foot valve in this pipe right?
If the water level is always up to the pump's inlet height, remove the check valve and put it on the outlet of the pump before the pressure tank. The pump will keep prime as long as the water in the aeartor is as high as the pump's inlet pipe and the check valve on the outlet will prevent the pressure tank from bleeding back through the pump into the aerator causing cycling of the pump on/off.
will I need an additional check valve here, I'm not sure air pressure won't force the water from my pump back into the aerator if I remove that valve. Doesn't the u-shape I created in the suction line assure part of the pipe will always be above the water level in the aerator and as the aerator's water level decreases wouldn't the jet pump/bladder tank spend a lot of time backfeeding to equalize pressure up to the height of the inlet on the jet pump, until the well pump caught up?
I don't like a pressure tank to be plumbed on a tee before the tank inlet. I like to go past the tank, feeding the tank off the main line to the house. That way the water flow direction does not have to change direction when the pump comes on or goes off, which causes water hammer when it does like in your design.
The outlet from the jet pump comes out of the top of the pump, turns vertical, then it runs down into the center leg on the tee...Are you saying to cut out that tee and place the house feed on the center leg of a new tee that way the water will flow one direction and branch off to the house or continue in a straight line to the tank as it chooses. Will this solve the problem?
I would not build or use any type of hammer arrestor, that treats the symptom rather than the cause and an air chamber type will allow the air to be absorbed into the water and that prevents it from working. Then you drain the water out of the system to get air back into the chamber; over and over'n over for ever.
ok
You should set the air pressure in the pressure tank to 28 psi with no water in the tank and then adjust the switch to 30/50.
Thanks
How do you control the water level in the aerator and the well pump?