Breaker ties do not make breakers common trip. They force the person turning off a breaker to turn off both (or all three) poles. With breaker ties installed between breakers, when out breaker trips, it will not open the other breaker.
Only two pole (or on 3Φ service, 3 pole breakers) purchased as one assembly will open all phases when one phase trips.