Thread: Are my "semi-shared neutrals" a problem?

  1. #1
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default Are my "semi-shared neutrals" a problem?

    I just installed a pair of 3-way switches for the two lights for my basement stairway. The power goes to the switch at the top of the stairs, and the lights are fed by the switch at the bottom. However, one side of the light at the bottom of the stairway is connected to a neutral for a circuit other than the circuit that services the switch and light at the top. This configuration was not planned. Rather, I simply missed the matter of running yet another wire to be able to connect the bottom light's neutral at the top.

    The two circuits involved are on opposing legs in the breaker panel.

    Question: Will what I have be okay as long as I install a double-pole breaker for those two circuits? Their respective loads are each small and essentially equal.

  2. #2

    Default

    No, this is an illegal connection and must be corrected if you want to comply with today's standards and be safe.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  3. #3
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by jar546 View Post
    No, this is an illegal connection and must be corrected if you want to comply with today's standards and be safe.
    Please try to help me understand what might be wrong or dangerous or whatever. Shared neutrals are not "illegal", and using a double-pole breaker for these two circuits would make it impossible for anyone to get hurt while working on either as long as the breaker is off.

  4. #4
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    If 2 separate circuits have a interconnected neutral and you shut off 1 circuit the circuit that is not off will keep the connected neutral "hot" because it is not off, it is still operating through the 2nd live circuit.

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    In a shared neutral, the assumption is that the two loads are nearyly balanced, thus the current in the neutral wire is small. In your case, alth0ugh your loads are small, as you describe, you have UNbalanced the load to some extent. Is is really dangerous? Maybe not. But codes are written to avoid "maybes" and protect against something that some future homeowner may do, unaware of the shared neutral.

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by leejosepho View Post
    what might be wrong or dangerous or whatever.
    It is very wrong for several reasons.

    One is that unless you are going to be the only person working on the circuit no other person will understand just what is going on with the circuit and will rewire the entire circuit

    Two all conductors of a circuit must be in the same raceway or cable. This stops inductive heating which can start a fire, see 300.3(B) of the NEC

    The list goes on and on but the simple answer is the installation does not comply with the safety standards of today’s codes and is improperly installed.

    If you were able to install the switch leg from the switches to the light it would be just as easy to install the grounded neutral with it so lets get this fixed right away.

  7. #7

    Default

    Ever hear the term "he knows just enough to be dangerous"?

    It applies here.


    Although it helps to understand why, it's prudent in this case just to take the advice offered here and do whatever it takes to wire your switches correctly.

  8. #8
    Remodel Contractor GabeS's Avatar
    Join Date
    Jan 2007
    Location
    Brooklyn NY
    Posts
    294

    Default

    Just curious. How do you guys wire a three way switch with 2 lights in between. Do you establish a regular 3 way connection with one of the lights and then just jump to the other light. And in that case can you just keep jumping to other lights if you want more than two?
    Gabe

    Don't follow my advice, I only know a thing or two about a thing or two.

  9. #9
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    It is ALWAYS easiest to run a 3-wire between switches. To go: switch-light-light-switch; you need a 4-wire between the lights.

    The physical relationship between the lights and switches is rarely a concern.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by GabeS View Post
    Just curious. How do you guys wire a three way switch with 2 lights in between.
    A three way switch is wired no differently than any other switch. The only difference between a three way (with a four way in between) and a single pole switch is the use of travelers which alternate between the switches.


    Quote Originally Posted by GabeS View Post
    Do you establish a regular 3 way connection with one of the lights and then just jump to the other light. And in that case can you just keep jumping to other lights if you want more than two?
    Yes there can be more than one light up to as many as the overcurrent device will carry.

    What Lee has done if very dangerous as he will now have current flowing through conductors that are not run together. When current is flowing through only one conductor it produces heat through induction.. Any metal that surrounds this single conductor such as metal boxes, staples, connectors and such will begin to heat. The more heat that is applied the more carbon will build up and the more carbon buildup the more heat that is produced and the carbon holds this heat. If two conductors are present in the cable or raceway that carries the same current, the two conductors will cancel each other out

    If there is nothing more learned by the Do-It-Yourselfer on this forum it MUST be that electricity will work even when it is installed in a very dangerous manner. There is ONLY ONE correct way to make an electrical installation that is safe to both persons and equipment and just making it work is not the correct way.
    If the person making the installation must ask this question they would be better advised to leave the work to someone else.
    Please try to help me understand what might be wrong or dangerous
    It is the lack of this knowledge that causes fires and death to the end user. A discussion forum is not the place for someone that does not understand the danger of electrical current to learn these dangers unless the discussion forum is set up in a classroom environment.
    As many professionals have said and I must say that I agree, it is those questions that do not get asked, or an explanation of the dangers that causes someone to get hurt or cause damage to the wiring system or the building in which it is installed.

  11. #11
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by Cass View Post
    If 2 separate circuits have a interconnected neutral and you shut off 1 circuit the circuit that is not off will keep the connected neutral "hot" because it is not off, it is still operating through the 2nd live circuit.
    Yes, and that was my very first thought just as soon as I realized I did not have the fourth wire Speedy Petey has mentioned ... and a double-pole breaker will resolve that "still operating through the 2nd live circuit" issue.

    Quote Originally Posted by jimbo View Post
    ... you have UNbalanced the load to some extent. Is is really dangerous? Maybe not. But codes are written to avoid "maybes" and protect against something that some future homeowner may do, unaware of the shared neutral.
    Understood, and this is not a final installation.

    Quote Originally Posted by jwelectric View Post
    It is very wrong ...
    No, just wrong (without the "very").

    Quote Originally Posted by jwelectric View Post
    If you were able to install the switch leg from the switches to the light it would be just as easy to install the grounded neutral with it so lets get this fixed right away.
    You bet, and it looks like all I need to do is to get about 30' of 4-conductor Romex or whatever.

    Quote Originally Posted by 220/221 View Post
    Ever hear the term "he knows just enough to be dangerous"?

    It applies here.
    Now there is a case of something or someone being *very* wrong! If what you have said were true, I would not be here asking questions!

    Quote Originally Posted by 220/221 View Post
    Although it helps to understand why, it's prudent in this case just to take the advice offered here and do whatever it takes to wire your switches correctly.
    Agreed, but I would still first have to know "Why?" in order to help assure not having to go back and change even more yet later on.

    Quote Originally Posted by jwelectric View Post
    ... he will now have current flowing through conductors that are not run together.
    Ah. That is yet another issue I did not know about ... and I will try to make and post a sketch to be sure I understand how things need to be.

  12. #12
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Here is a sketch of what I have at the moment ...

    I also have a bare ground connected everywhere, of course, but it is not shown in the sketch.
    Attached Images Attached Images  
    Last edited by leejosepho; 12-28-2008 at 02:00 AM. Reason: sketch updated

  13. #13
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by leejosepho View Post
    Here is a sketch of what I have at the moment ...

    I also have a bare ground connected everywhere, of course, but it is not shown in the sketch.
    Lee have you ever heard this statement?

    Quote Originally Posted by 220/221 View Post
    Ever hear the term "he knows just enough to be dangerous"?

    It applies here.
    You have a serious problem with this installation and it needs to be addressed now.

  14. #14

    Default

    Quote Originally Posted by Speedy Petey View Post
    It is ALWAYS easiest to run a 3-wire between switches. To go: switch-light-light-switch; you need a 4-wire between the lights.

    The physical relationship between the lights and switches is rarely a concern.
    See this crude drawing: http://www.remasinspections.com/images/3wayswitch.pdf
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  15. #15
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by jwelectric View Post
    You have a serious problem with this installation ...
    Please elaborate, you old windbag!

    I am trying to be sure I get this right, and you have only editorial comment to offer. Has it ever crossed your mind to actually try to be helpful?!

    I have one light sharing a common, and that needs to be corrected.

    What is the alleged "serious problem" you have mentioned?

    Your wife is correct.
    Last edited by Cookie; 12-27-2008 at 10:49 AM.