    OK, professional plumbers. How you you pressure test your PVC or ABS DWV systems when required for inspection?

    I think we can get a good conversation out of this subject.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  2. #2
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    lots of gun powder down the stack.


    BUt really we fill the whole system with water. You have test balls and caps and test plugs blocking off the openings.

  3. #3

    Default

    I am bringing this up because the IPC and IRC have a water method and air pressure test. The compressed air test seems to be the most popular but the plastic pipe industry does not allow it even though it is widespread.

    Many times on jobsites, there is no waterflow because there is a well and it is often not ready for use when the plumbing rough is due.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  4. #4
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    Good point about the well. I have ran into homes that needed the DWV tested, but there was no water service yet, so I went to the village and got a fire hydrant meter and used the hydrant for our water source.

    Found this technical bulletin about air testing. http://www.pweagleinc.com/literature/tb/tb-i2.pdf
    Last edited by SewerRatz; 12-21-2008 at 09:20 PM. Reason: Added a link

  5. #5
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    99% of the time we use air @5lbs. Manufactureres don't like you pumping foam core pvc up past 7 lbs. Water is a huge pain in the you know what, but occasionally necessary.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default test

    Water. It is easier to find a leak, often at a cleanout plug, than air. And if it is a stubborn cleanout plug that will not seal, the inspector can see it and will usually not reject it. That would not be the case with air.

  7. #7
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    I once caught a plumber gluing the plugs on the clean outs. I was like WTF man are you crazy?!?! Apparently he never did service work. The inspectors learned of his practice and made him go back on 100's of jobs to correct this issue.