    My father-in-law has a machine in his shop that runs off an electric motor . There is a plate on the motor that has diagrams that shows how to wire the motor for 120 v or 240 v . The motor has 4 wires coming out that are numbered 1-2-3-4 . For the 240 v connection it shows 2&3 together & 1 & 4 connecting to L 1 & L2 . That's the way it was wired when he got it , however he hooked it up to 120 v & it ran . For the 120 v connection it shows 1&2 connected to L 1 & 3&4 connected to L 2 . Since he wanted to run it on 120 I switched the motor wiring to match the 120 v diagram . It wouldn't run so I switched it back . It was getting late in the evening so I didn't check amperage , rpm , ect . I haven't been back to do any further checking so you now know as much as I do . Ideas , opinions ????

  2. #2
    Electrician frenchelectrican's Avatar
    Join Date
    Jun 2007
    Location
    NE Wis / Paris France { In France now }
    Posts
    46

    Default

    If my memorey serve me right you need to hook 1,3 to L1 and 2,4 to L2 that for 120 volts connections

    before you do anything more do you know what motor manufacter it is ?


    I pretty sure this is one of older motor style which I haven't see it for while.

    Merci,Marc

  3. #3

    Default

    Your post does not make sense. You said that it worked when wired for 120v then switched it to 120v and it would not work. Do you mean you tried it at 240v?

    You will have to change your breaker and the setup in the breaker panel when you change from 120 to 240.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  4. #4
    DIY Senior Member WV Hillbilly's Avatar
    Join Date
    Aug 2008
    Location
    WV
    Posts
    178

    Default

    No didn't try it at 240 . This machine is one my father-in-law just got . I was at his house for a different reason & didn't spend much time fooling with the machine . Where he placed the machine in his shop is right beside a 120 v receptacle . It pulls 13.6 amps wired for 120 . There is a 3 wire cord to connect to line voltage . One wire is a ground & the other 2 go into the motor through a fused on / off switch . He stuck the two motor wires in this cord into the power & neutral slots on the 120 v receptacle & the motor ran but the diagram on the motor showed it was wired for 240 v . I'm wondering why it didn't run when I switched the wires on the motor to match the 120 v diagram .

  5. #5

    Default

    The motor has two windings, each of which is made to operate at 120v. Connecting 2&3 together puts the windings in series, which means that if you apply 240 volts each winding gets 120v. When you connect 1&3 and 2&4 together the windings are in parallel, and they need 120v applied. This is what Marc was saying in his post. I suspect that you may have misread the wiring diagram, and would suggest that you take a closer look at it when you get a chance. Here's a crude drawing that I slapped together that should help to explain how this works.

    Name:  Motor-Connection.jpg
Views: 2461
Size:  11.0 KB

  6. #6
    DIY Senior Member WV Hillbilly's Avatar
    Join Date
    Aug 2008
    Location
    WV
    Posts
    178

    Default

    Thanks , makes perfectly good sence . The machine & motor are pretty old & the diagram was pretty hard to read so I probably misread it . The motor wires have metal clamps around them with numbers stamped in the clamps so they are not hard to read . Would a motor such as this likely run on 120 if it's wired for 240 at the motor ? I realize if the answer is yes the motor likely wouldn't be running properly .

  7. #7

    Default

    It depends mostly on the load. If the load was light enough that the motor could get running and up to speed in a short time, then yes, it would run.