    I need some advice, I'm an average DIYer, but this has me puzzled. I installed 3 sinks in a salon last week. I had a licensed plumber install the drains, feed lines and vents. When I installed the sinks they did not line up with the drains in the walls and the drains were lower than the exit from the p-trap. So from the exit of the p-trap I installed a 45 on an angle twords the drain and then another 45 at the drain and ran a piece of pvc pipe between the two... This seemed to me to be the easiest thing to make the drain and the p-trap come together.

    Yesterday the plumbing inspector showed up and said that this was "very, very bad", making the owner of the salon panic... what did I do wrong? He is saying that the drain is going up? I should have taken pictures when I was there today, and I will before I start over on Sunday.

  2. #2
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    The trap arm needs to head directly to the T in the wall...If the sinks pop up tail piece is to high use a tail piece extension to reach the trap then go directly to the wall with a little pitch...

  3. #3
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    Quote Originally Posted by mhaines View Post
    I need some advice, I'm an average DIYer, but this has me puzzled. I installed 3 sinks in a salon last week. I had a licensed plumber install the drains, feed lines and vents. When I installed the sinks they did not line up with the drains in the walls and the drains were lower than the exit from the p-trap. So from the exit of the p-trap I installed a 45 on an angle twords the drain and then another 45 at the drain and ran a piece of pvc pipe between the two... This seemed to me to be the easiest thing to make the drain and the p-trap come together.

    Yesterday the plumbing inspector showed up and said that this was "very, very bad", making the owner of the salon panic... what did I do wrong? He is saying that the drain is going up? I should have taken pictures when I was there today, and I will before I start over on Sunday.
    Absent pictures, can you post a drawing or something? Having a hard time picturing what you did.
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...
    __________________
    Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.

  4. #4
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,245

    Default

    If the drain was too high, you'd have a real problem, but since the drain is lower than the P trap, all you need is the extension that Cass spoke of. In theory you need a slope of 1/2" per foot on a drain, but for the short distance from the P trap to the drain, you don't have to get too finite about that, just don't go up to the drain nor make it too steep of a pitch which is what you have now.

  5. #5
    Network Engineer rmelo99's Avatar
    Join Date
    Jul 2006
    Location
    Connecticut
    Posts
    349

    Default

    It sounds to me like you did the opposite of what most do when plumbing a p-trap that isn't at the right height.

    The exit from the p-trap should go straight into the wall (meaning a lower height than you have now on the p-trap), then you will have a gap or shortage coming from the tailpiece on the sink that won't reach the top of the p-trap. Like Cass said then you just extend the vertical tail-piece down with a tail-piece extension.

    I'm just a DIY'er, not a pro. Pics would help just incase we're not getting something specific to your installation

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,379

    Default

    Hair washing sinks can be quite deep. It sounds to me like you went from the p-trap and angled up to get to the connection in the wall. Well, if so, that is a major pain...the connection in the wall needs to be lowered. As said, you can't go UP from the outlet of the p-trap.

    Unless you can shorten the tailpiece of the sink to raise the p-trap location, the only way to fix this is to get the plumber to lower the connection in the wall.

    A picture would really help...
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    In the Trades Master Plumber 101's Avatar
    Join Date
    Aug 2008
    Location
    Wisconsin
    Posts
    268

    Default You shouldn't do plumbing.

    It sounds to me you need an extension tail piece. Next, under no circumstance should the owner of a comercial business do any type of plumbing other than a basic faucet repair. I can also assume that the plumbing contractor pulled permits for the job. He should of completed the job from start to finish. You may have to pay some extra money out of pocket. I hope you learn from this experience.
    "Labor create's all wealth and therefore that all wealth belong's to Labor"

  8. #8
    Plunger/TurdPuncher kingsotall's Avatar
    Join Date
    Aug 2008
    Location
    Flagstaff, AZ Sitting on an upside down 5 gallon bucket next to the GO 68HD
    Posts
    1,260

    Default

    When we did a grease trap replacement I recall when I was doing some studying that a hair salon/barbershop needs a sediment trap or something along those lines...

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default drains

    What is a DIYer doing plumbing in a commercial establishment. In most cases even the proprietor cannot do it himself unless he owns the building, and then HE has to do the work he cannot hire someone else. You need hair traps on the shampoo sinks, not P traps.

  10. #10
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    You upward turn created an unvented s-trap.
    As HJ stated you also need hair traps installed, and being unlicensed you have no business plumbing in a commercial establishment. The hair salon owner needs to get the original plumber back to complete the job!