    Lightbulb PUMP can effect to main circuit breaker get trip?

    We have 3 chillers, 3 CHWP and 3 CDWP dedicated for office tower building load.

    Chiller technical room is at roof floor.

    When we run all CDWP, it is fine.

    If we start running one CHWP, that is fine also.

    But if we run 2 CHWP, one CHWP will make main circuit breaker get trip.

    Note: breaker calibration is 150%[160A] higher than normal rated Amp.
    - Cable line to each pump is fine, around 30 or 38 DegC
    - During Breaker get trip, max rated Amp=80A
    - CHWP- Chilled Water Pump
    - CDWP- Condenser Water Pump

    Could you kindly advice?
    Does the pump motor get problem?
    Does the alignment pump get problem?
    Does the surge pressure head can effect to motor overload?

    Very thanks for your advice and comment.

    Chomnap

  2. #2
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    Were you able in the past to do this and all of a sudden you no longer can or is this all a new install.

  3. #3

    Default

    To do some troubleshooting we need to know what the load amps are on the motors. I would also recommend having a amp probe on the breaker to measure the amps when starting each motor.

  4. #4
    DIY Junior Member
    Join Date
    Dec 2008
    Location
    cambodia
    Posts
    6

    Default

    Hi Pump man,
    The rated Amp of motor are 103A.
    Note: Pump motor is equiped with VSD.
    MCB reated 150A {GV7-RE150}.

    Kindly let me know your idea?

    Very thanks for your help......

    Enjoy your day!

  5. #5
    DIY Junior Member
    Join Date
    Dec 2008
    Location
    cambodia
    Posts
    6

    Default

    Hi Cass,
    This site is new building installation.
    we face this problem during Testing and Commissioning period.

    Note: We used existing chiller with New Chilled Water Pump.
    the problem is chilled water pump MCB GV7-RE150 is always trip even start-up and stop.

    Thanks for your help.

    Nap

  6. #6
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    These kind of problems are nearly always caused by the VSD. You probably do not have the correct shielded cable, or the grounding in not adequate. It could also be the combined harmonics from the two pumps. Harmonics cause "dirty power" to go back into the electric grid. This increases amperage and heat in the breakers and transformers.

    VSD's are suppose to save energy but, they don't. Usually the VSD is such short lived, causes so many problems, and cost so much to maintain or replace, that you can never save enough energy to justify the cost of the VSD. Sizing the pump correctly and using a simple valve for flow control can save just as much energy, last much longer, cost less, and doesn't give the problems associated with VSD control.