Thread: Gas step down

  1. #1
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default Gas step down

    I have a gas pipe runninig straight to my boiler from the main. Halfway through the run there is a tee. The tee is capped on one end for future expansion. The tee is reducing the second connection ( The capped one). What is the purpose of the reduce in size? Will there be sufficient flow to the expansion branch to a new stove (duel fuel burners only) if this is utilized? If the sizes are important for this question I can get that tonight. Just wanted to understand the physics behind this.

    Thank-you

  2. #2
    DIY Senior Member jastori's Avatar
    Join Date
    May 2008
    Location
    Illinois
    Posts
    118

    Default

    Generally, gas piping should be sized correctly for the appliances that are to be supplied for each branch. The branch lines need to be "large enough" to supply the necessary gas volume without too large of a pressure drop. Having oversized gas lines is not likely to be a problem, but having them undersized would be. Sizing the lines properly requires using published tables from the fuel gas code, or other sources.

    The person who installed the "T" probably believed that the reduced size branch would be adequate for the anticipated expansion. Whether it is or not, depends on the size of the branch, total length of piping from the appliance to the gas meter, and other factors such as the supply requirements of the boiler, size of the line prior to the "T", etc.

    If the reduced size "T" outlet is 3/4" nominal iron pipe, it is very likely adequate to supply a stove. If it is 1/2" diameter, it may still be adequate. Determining this would require someone who has access to the tables, and knows how to use them.

    Please keep in mind that gas is dangerous, and if you are doing the work yourself, you definitely need to do proper testing, including a permit and inspection. Many areas do not permit homeowners to do their own gas work.