Thread: Intermittent ignition on W-M boiler, Beckett AF oil burner

Hybrid View

  1. #1

    Default Intermittent ignition on W-M boiler, Beckett AF oil burner

    We had our unit's annual service several weeks ago. This included the full complement - cleaning, new filter, nozzle, igniter gap check, etc. Since the heating season has started there are many times when the unit attempts to light and then times out. If I hit the reset button it will sometimes light, but if not, while attempting to light, I can get it running by inserting a propane torch into the inspection port.
    Yesterday I removed the electrode assembly after some difficulty as the splined nut that holds it tight to the escutchion plate seemed misthreaded. I cleaned the electrode insulators (were covered with soot and "tar"), adjusted the gap which was pretty close to specs, and replaced the connector tube with a new one. The rest of the day yesterday the unit lit promptly, and I was cautiously patting myself on the the back.
    Of course, this morning it failed to light until I hit the reset button and it started up fine.
    One thing i did notice yesterday is that the igniter tips are fairly blunt. Are they supposed to be sharp points?
    I'd appreciate any thoughts before calling the company for a service call. Thanks loads!

  2. #2
    Master Plumber nhmaster's Avatar
    Join Date
    Jul 2008
    Location
    S. Maine
    Posts
    2,039

    Default

    Think I'll need the optional chin strap for this one boys.



    Call a HEATING TECHNICIAN before you burn you house down.

  3. #3
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Quote Originally Posted by Baltimore Lou View Post
    I'd appreciate any thoughts before calling the company for a service call.
    Call them now! Sheesh!

  4. #4

    Smile Service tech just left...

    after replacing the transformer. System is now working fine. Your advice, while blunt, was appreciated. Thanks!

  5. #5
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Thank you for calling them.
    You were treading on dangerous ground.