    Default T & P valve disharge pipe into laundry tub

    Hot Water tank is in finished basement level. I.m always thinking..'what if the tp valve blew'
    So i.m thinking of running it about 10' of pipe ( plus 1 elbow) or so over into the laundry tub, then if for some reason it blows off it won't flood my basement floor (carpetting etc.)
    Is there any law preventing this or is this a wise move? thanks for any reply

  2. #2
    Plumber, Contractor, Attorney LonnythePlumber's Avatar
    Join Date
    Sep 2004
    Location
    Wichita, Kansas
    Posts
    319

    Default Someone Answer

    I think it is okay but I'm not sure so I'm hesitant to guess.

  3. #3
    Architect Spaceman Spiff's Avatar
    Join Date
    Aug 2004
    Location
    Salt Lake City, Utah
    Posts
    277

    Default

    Oops, guess I shouldn't post when I'm tired.
    2003 UPC:
    504.6.1 Discharge. The relief valve shall discharge full size
    to a safe place of disposal such as the floor, outside the building,
    or an indirect waste receptor. The discharge pipe shall
    not have any trapped sections and shall have a visible air gap
    or air gap fitting located in the same room as the water
    heater. The outlet end of the discharge pipe shall not be
    threaded and such discharge pipe shall not have a valve or
    tee installed. Relief valve piping shall be piped --->independent
    of other equipment drains<--- or relief valve discharge piping to
    the disposal point. Such pipe shall be installed in a manner
    that --->does not cause personal injury to occupants<--- in the immediate
    area or structural damage to the building.

    You could go to a floor drain...
    Last edited by Spaceman Spiff; 10-09-2004 at 02:00 PM.
    Spaceman Spiff aka Mike

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,550

    Default t&p

    It would not pass here, because the laundry sink is an appliance that could be in use by someone when the discharge occured, probably scalding them. Here it has to be piped to the exterior of the building, to a floor sink, or to a mop sink on the floor that no one would be washing their hands in it at the time.

  5. #5
    DIY Senior Member Hube's Avatar
    Join Date
    Sep 2004
    Location
    Ontario
    Posts
    156

    Default

    Thanks, for the info. Hube