AC in attic?

Users who are viewing this thread

jmbig

New Member
Messages
1
Reaction score
0
Points
0
My daughter is considering buying a small ranch which has hydronic heating and thus no ductwork. Is is possible to install an AC unit in the attic with smaller vents placed in the ceilings of the rooms below? Are there any special units for this? Certain brands? The house is in northern Ohio so the ac is only necessary for a maximum of 3-4 months/year. Thanks.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
You can do this. You could put an air handler up there and the compressor outside. If you go with high-velocity ducts, the outlets are small. An alternative that works if the layout is fairly open is a split system. This has a unit with (usually) multiple compressors mounted outside, and indivdual fans and evaporators inside. Some can handle up to three zones. The units do take up some wall space, but are quiet since they only contain the evaporator and an air circulator fan. Often, they are mounted high on the wall and are controlled via a remote that also acts as a thermostat.

Putting the compressor in the attic isn't probably a great idea, it's already hot enough and it gets inefficient dumping the waste heat up there. It could be mounted on the roof, but servicing is tough and the roof may not be designed for the weight along with a snow load.
 

BurleyMike

New Member
Messages
118
Reaction score
0
Points
0
Location
SE Idaho
It is done all the time espically in the southern states. I have done a few of them. The only hard part is getting the air handler up there sometimes you have to increase the size of the attic access. Of course the duct work needs to be insulated since the attic is not conditioned.

You might consider installing heat strips in the unit for a backup heat if the main system fails. Of course this depends on the electric service coming into the house. Just a thought.

Be sure to get several bids from independant contractors. A lot of those big chain type plaes have big chain type prices.
 

Furd

Engineer
Messages
448
Reaction score
1
Points
16
Location
Wet side of Washington State
Air handler and ductwork in the attic along with registers in the ceiling is common. The condensing unit (compressor) will be mounted outside on the ground.

Be careful if you decide on using a high velocity system as they tend to be noisy unless carefully designed and installed.

You absolutely MUST have a heat load calculation done to properly size the unit. Oversized is usually worse than undersized because it will not properly remove the humidity.
 