Got a question for ya. This is Bill Julian. (Plumber) How would I pipe 3 hot water heaters so I don't create a reverse loop and they draw equally together. I have 3 120 gallon heaters. I'm told by the inspector that I am over working one heater the system is not equally drawing. Said something about a reverse loop and the tees have to situated correctly.

All the colds got in series all the hots come out in series I have the hot 3/4 tee to fixtures near the end of the 3rd heater.

Thanks

Bill
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
You say series, but it sounds like you mean the 3 tanks are parallel. In this case, the inlets and outlets must be manifolded so they are identical.
 

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
3 120 gallon water heaters

Sounds like you have eather A.O. Smith cyclone or STATE water heaters
go to hotwater.com web site,
for A.O. Smith and they will show diagram of the
proper way to pipe as they are supposed to be per, mfg's spec's and plumbing code also you can call 1-800-527-1953 for tech, support ! !

Do not forget to make sure you have the proper sized thermal expansion tanks
installed for all three heaters
 

SewerRatz

Illinois Licensed Plumber
Messages
1,681
Reaction score
10
Points
38
Location
Chicago, IL
Website
www.a-archer.net
As Mark asked "what are you doing anyway, is this some sort of hotel??? " How many fixtures are in this building and how many people are in it? Three Gal heaters is insane. If it is a hotel or a place that needs real fast recovery why not use a 200 Gal storage tank a A.O. Smith Burkay boiler with a recirculate pump. I had a restaurant in Chicago that has this set up installed. I had to replace the 20 year old storage tank, once I refilled the system and fired it up they had 180 degree water in 12 minutes. Another option is tankless heaters.

Here is a couple pictures showing tankless heaters installs one is gas other is electric.
ganged.jpg


sewerratz-01.jpg


With more information about the job like if your using gas fired heaters and the BTU's of each heater, or if they are electric, and how many fixture units is the demand on this place. Then we can give you a more accurate answer on how to install what you want.

Here is a link to A.O Smith's recommended way to install multiple heaters in parallel. But each manifold MUST BE EQUAL LENGTH or it will not work.
 
Last edited by a moderator:

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
heaters

You get either the State #27200 or A O Smith #70415 three tank manifold kits, or you get their specifications and make your own. Once you see the prices you will know why this is not a "by the seat of your pants" task.
 