    I had a breaker that did not trip. There was a loose connectionin on a lug, the lug had a darkened color due to the arcing which produced heat. The question I have is why did the breaker not trip?

  2. #2

    Default

    Is it a Federal Pacific Stab-Lok panel?

    A loose lug on the breaker could have been a contributing factor.

    Now the breaker needs to be replaced.

    If it was a high amperage breaker, there could be enough heat to cause discoloration on the lugs but not trip due to lack of enough amperage sensed inside the breaker.

    Many possibilities
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Was there a short circuit which SHOULD have caused the breaker to trip? A loose connection can arc under normal current draw. The breaker does not see this as a fault which it should trip/

  4. #4
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    A loose connection can only reduce the current in a circuit, so it's possible there really was not enough amperage to trip the breaker.
    In this case power that is supposed to go into the load goes into heating the bad connection.

  5. #5

    Default

    It was not Federal Pacific Stab-Lok panel. It was in GE breaker panel.

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    only an arc fault would have tripped

  7. #7

    Default

    Standard breakers trip when too much current flows thru them.

    Arcing and burning can easily occur with current flow under it's rated max.

  8. #8
    Electrician Johnny C's Avatar
    Join Date
    Oct 2008
    Location
    Mass. & now Virginia Beach, VA
    Posts
    23

    Default Breaker didn't trip

    A faulty connection at the breaker terminal offers resistance to the flow of current thereby limiting the amount of current passing through the breaker. So the breaker doesn't trip due to high current. However, I have investigated instances where the heat generated by the bad connection caused the breaker to trip due to the transfer of heat from the fault into the heat sensing element in the circuit breaker.

  9. #9

    Default

    Thanks for your advice!

  10. #10
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by edstevn View Post
    the lug had a darkened color due to the arcing which produced heat.
    You might want to replace the breaker.