    I have caused my self some headache. I had to dig up my well head to add a pitless adapter that was left out by the installer. In the process some dirt fell into my well. (I found an old license plate cut to block the oversized hole in the side of my well pipe) My pump has sucked some gravel and the system won't hold pressure. I pulled my pump up, it is a 110v sears 40/60, but I can't find the check valve. Is it in the pump, if so is it serviceable?

  2. #2
    Previous member
    Join Date
    Jul 2005
    Location
    Riverview, Fl.
    Posts
    4,540

    Default

    Your going to have to send some pictures or give a better description of what you have before I can help.

    bob...

  3. #3
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    When you say it won't hold pressure, do you mean when the pump shuts off the gauge shows the pressure falling until the pump comes on again? Is that why you question the check valve, do you think it isn't closing?

    You only need a pitless adapter if you are in a freeze area.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  4. #4

    Default

    thanks for your interest. I live out in the woods in alaska and my dial up internet would take all day to send a picture. If I can't describe it better I will try a picture. The pump is 34 long 3.75 d the motor is on the bottom and the intake is in the middle. The motor bolts are in the intake channel. The casing is stainless. At the top of the pump is a cast cone that necks down to 1" npt, on the side of the cone is a 5/16 bolt. I would assume the check valve has to be above the pump, but the top cone seams crimped on. If there is one in line I can't find it.

  5. #5

    Default

    Gary, yes the pressure dumps in about 3 sec from 60-40 then back up when the switch kicks in. If I shut off the breaker it will go to zero. I live in alaska, it freezes.

  6. #6
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    You can buy an inline spring loaded check valve and screw it in/on the pump's outlet if you can't get the internal one off or out. Although if the old one falls just right in its housing it can reduce flow.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •