The system is as follows: 5/8" meter - 70psi - 3/4" PVB to a 1" PVC mainline to Orbits manifold (I told my friend to get Rainbird valves and I would build him a manifold) - way under 15GPM per valve; With the mainline under pressure there are no leaks. When he opens a valve, the PVB has water draining from the bonnet area and there is not enough pressure to fully operate Rainbird popups (they spray only a foot or so). Could this be caused by debris somewhere in the bonnet area of the PVB?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
The leak from the vacuum breaker prevents the downstream pressure from building up enough to "pop" the pop-ups. Repair the vacuum breaker.
 