The installer needs at least six feet for the flex connector on the stacking gas dryer.
Can I use two 48" flexes and connect them together?
I find anything longer than 48"
B Lewis
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
No, but you can get a 6' piece of csst and the fittings thouth without a license no one will sell it to you.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Csst

No, but you can get a 6' piece of csst and the fittings thouth without a license no one will sell it to you.

Please read your CSST manufacturer's manual. It states that CSST CANNOT be used as an appliance connector.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
No, but it can be used to extend the existing pipe and then a short appliance connector can be attached to it. sorry for not being specific enough.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
I have seen 6 footers in the 5/8 size for ranges. I have not seen a 6 footer in the 1//4 " for dryers. You definitely cannot put two together. It would be a fairly simple matter to put an elbow ahead of the gas valve and run a pipe vertically say 4', then put the valve up there.

Naturally, that pipe would be secured to the wall in some way, and as with ALL gas work, you have to pull a permit on this.
 