Thread: Dishwasher and disposal same box

  1. #1
    DIY Junior Member Steven Palmisano's Avatar
    Join Date
    Jan 2007
    Location
    Florida
    Posts
    25

    Default Dishwasher and disposal same box

    The wire that is in-place to supply the dishwasher, can I jump off of it to run a connection to a future disposal? I was thinking that I could hook both to a junction box, run a switch for the Disposal and put plugs on both appliances and plug into the receptacle.

    Thanks,

    Steve

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    210.23(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.

  3. #3
    DIY Junior Member Steven Palmisano's Avatar
    Join Date
    Jan 2007
    Location
    Florida
    Posts
    25

    Default

    Thanks...that sounds like "no' to me

  4. #4
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by Steven Palmisano View Post
    Thanks...that sounds like "no' to me

    Depends. what size wire is supplying the dishwasher and what is the load of the dishwasher? More than likely your good to go.

  5. #5
    DIY Junior Member Steven Palmisano's Avatar
    Join Date
    Jan 2007
    Location
    Florida
    Posts
    25

    Default

    Not sure Chris...I would quess typical wiring, and same typical DW and Disp. draw

    thanks

  6. #6
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    I think you have to parse the sentence from the NEC to see if it works.

    The first question is, what is meant by "fastened in place". It is important to note that a piece of equipment can be both cord-and-plug-connected and fastened in place.

    210.23(A)(1) discusses requirements for cord-and-plug-connected equipment not fastened in place.

    210.23(A)(2) discusses utilization equipment that is fastened in place, and the restrictions on load where lighting units and/or cord-and-plug-connected equipment not fastened in place is also supplied.

    Every dishwasher (except the roll-around kind) and every disposer that I have ever seen was fastened in place. A dishwasher that I installed last week was fastened to the bottom of the countertop, and the disposer was certainly fastened in place at the bottom of the sink. In that case, the restriction of 210.23(A)(2) does not apply.

    Therefore, the limit on whether you can connect a dishwasher and a disposer to the same circuit depends on whether the total load exceeds the branch circuit rating.

    My dishwasher is rated at 11.5 Amps and the disposer at 8.1 Amps for a toal of 19.6 Amps. They are both legally connected (hard-wired) to a 20 Amp circuit (circa 1965).

    One restriction on using a receptacle is that there is a code section (I am not going to search for it now.) that requires that cords for appliances be provided or approved by the appliance manufacturer. Most dishwashers and disposers don't come with cords. I would plan on using a piece of AC or MC, or LFNC.

    In the new house where I installed the dishwasher last week the licensed electrician had provided a 5 ft length of 14/2 NM (Romex) coming up through the floor at the back of the dishwasher space.

  7. #7
    DIY Senior Member taysan's Avatar
    Join Date
    Apr 2008
    Location
    Toronto, ON Canada
    Posts
    106

    Default

    And from a layman's practical point of view, how often are you going to want to run your dishwasher and disposal unit at the same time anyhow? You'd need ear protection.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default outlet

    The two appliances are connected to the same circuit more times than thye are separate.

  9. #9
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    I beg to disagree with everyone... the NEC also says, I believe, that appliances have to be installed according to the manufacturer' instructions?

    I've never seen dishwasher installation instuctions that didn't call for a dedicated circuit.

    So, while it'd probably work (because, as pointed out, what are the odds you'd run them at the same time?)... it wouldn't be legal.
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...
    __________________
    Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.

  10. #10
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default You're seeing one now...

    My Kenmore DW installation instructions' Electrical Requirements are:

    You must have:
    o 120-volt, 60Hz, AC-only, 15 or 20 amp., fused electrical supply.
    o Copper wire only.

    We recommend:
    o A time-delay fuse or circuit breaker.
    o A separate circuit.

  11. #11
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    Quote Originally Posted by taysan View Post
    And from a layman's practical point of view, how often are you going to want to run your dishwasher and disposal unit at the same time anyhow?
    Actually, I've often thought it might be a good idea to run the disposer during the dishwasher's drain cycle, to thoroughly grind up any big pieces left by the dishwasher's macerator (I think it's got one). Noise is not a big deal these days, but the total current required was a deal-killer.

  12. #12

    Default

    can I jump off of it to run a connection to a future disposal?
    More than likely, you can.


    All DW/Disp here share a dedicated 20 amp circuit. If it is an older home and the DW circuit has other stuff on it you would be pushing it.

  13. #13
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default disposer

    The big chunks, and little ones also will stay in the disposer and then be ground up the next time you operate it.

  14. #14
    Electrician Johnny C's Avatar
    Join Date
    Oct 2008
    Location
    Mass. & now Virginia Beach, VA
    Posts
    23

    Default Dishwasher and Disposal on same circ.

    Good answer "Frenchie". UL listed product must be installed in accordance the their Labeling and Listing requirements, NEC 110-3(B).