Sjsmithjr
In the Trades
For the life of me I can't fish the runs (NM) from a laundry room addition the last couple of feet back to the service panel. The service panel is mounted on an exterior wall. Is there a code compliant way come in the side of the box the last couple of feet via conduit? As I understand it 2x12-2 and 1x10-4 NM would violate the conduit fill rule. Is it permissible to strip the jacket once the NM enters the conduit?
Thanks.
Thanks.