Results 1 to 6 of 6
Thread: Branch Circuit Partial Run in Conduit
    Geologist sjsmithjr's Avatar
    Dec 2005
    Knoxville, Tennessee
    Default Branch Circuit Partial Run in Conduit
    For the life of me I can't fish the runs (NM) from a laundry room addition the last couple of feet back to the service panel. The service panel is mounted on an exterior wall. Is there a code compliant way come in the side of the box the last couple of feet via conduit? As I understand it 2x12-2 and 1x10-4 NM would violate the conduit fill rule. Is it permissible to strip the jacket once the NM enters the conduit?
    Thanks.
    -Sam Smith
    Licensed Professional Geologist - AL, TN, KY
    Default ?
    Use larger conduit.
    Dec 2005
    I'm guilty of not provided sufficient information again. I believe 2x12-2 and 1x10-4 NM would overfill 2-inch conduit, and 2-inch is the largest I can run.
    -Sam Smith
    Jun 2007
    North Carolina
    Can't run NM on the outside no matter what kind or size pipe you install
    Dec 2005
    Understood. I take it then the right way is to run NM to a junction box, then THHN from the box in conduit to the service panel?
    Bummer of a week for the electrician in the family to be out of pocket...
    Thanks,
    -Sam Smith
    Electrician Johnny C's Avatar
    Oct 2008
    Mass. & now Virginia Beach, VA
    Default Power supply to Panelboard
    Use type NM cable for the interior wiring to a "J box" and run conduit on the outside of the building with THWN or XHHW. The conductors must be suitable for a wet location.