I have a steam system in a 2 floor house with a basement. It has a dry return. When the heat goes on all the radiators work fine, but one of the radiators on the second floor for some reason fills up with water and starts leaking from some of the joints. While the heat was on I took off the air valve and water started gushing out. I can't figure out for the life of me how water is filling up in the radiator that's on the second floor!! Somebody please give me some ideas so I can fix this myself. I have intermediate knowledge of steam systems.

The shutoff valve is also new so I know it's not clogged, the water should be returning and the radiator leans slightly toward the shutoff valve for the water to return.

Congratulations to the person who knows what the problem is and walks me through this one. I have to say I'm a little skeptical. I've already asked half a dozen people and no one could explain this phonomona.

Gabe
 

sibi1972

New Member
Messages
32
Reaction score
0
Points
0
Gabe,

What I know about steam heat fits easily into a thimble so maybe I shouldn't ask this but here goes.

If the vent on that radiator is working correctly then is it possible that the return line is just plain clogged somehow or that it doesn't pitch the way it needs to?

I know those radiators aren't easy to remove but if you did remove it you might be able to see what's going wrong there. Provided your sure everything else is working as intended.

BUT - if the real answer is NO stupid, this is what it is, then that's OK with me because I don't know anything about steam heat but would learn something along with you.

Sibi
 
Last edited:

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
To understand where the water comes from you've got to understand a few very simple concepts. The boiler heats water and makes steam (water vapor), which is under pressure so moves up to the radiators.

When the steam reaches the colder radiator it releases its heat and condenses inside the radiator. In other words, it turns back to liquid water, or "condensate". The liquid fills the bottom of the radiator and drains down the return line. These pipes should drain by gravity back down to the boiler. There should be a pump and check valve to get the condensate back into the boiler.

Since you have water filling up a single radiator that means that you have a clog somewhere in that portion of the return system. Most likely it is due to corrosion products (rust) or deposition products (lime scale). It depends on your water. If you have hard water it's lime, otherwise it's rust.

A pro might be able to add chemicals to disolve the crud, back flush the system and clean it out that way. If not its time for disassembly and cleaning. A pro might also recommend treatment chemicals to add to the boiler after its all working again to reduce the corrosion or lime scale build-up in the system.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
If your radiators have a trap on the return side the thermostatic disc eventually gives out and needs to be replaced. This element opens when hot water hits it and lets the water return to the boiler either by gravity or a condensate pump. For residential applications, gravity is much more common. To test the trap, fire the system up and feel the outlet pipe below the trap. If the feed pipe to the radiator is hot and the outlet pipe is cold then the trap element is bad. The other possibility is that the wet return pipe is plugged with rust. Very common and typically when they get to that point the pipe is about ready to start leaking and should be replaced. Then again by the time you do all that it may be time to think about converting it to forced hot water and save yourself some money on the old fuel bill. Very few things are less efficient than steam.
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
there are no trap or pumps on any of the return lines. Just strictly piping.

It might be a clogged return line on that specific radiator. If so, would that explain that water shooting out of the side when I remove the air valve. Where would the build up most likely be (near the shutoff valve, or first elbow, or could it be anywhere on the line?)

Also, what are some of the better products used to clean the piping and boiler and what is the best way to go about this?

I have an old cast iron weill mclain boiler.

Thanks.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
When the boiler is on, the heat causes steam which expands, and will pressurize things somewhat. Therefore, when you open up the bleed valve, it, along with the head pressure if the radiator is full, will help to push the liquid out.

I think you'll have a hard time injecting a chemical into the system to try to dissolve the rust...it will probably release enough that is on the walls of the pipe to create more problems.

Unless you lose water (in most systems, you aren't supposed to), after a fairly short time, you've reached equilibrium - you've used up all of the free oxygen in the water and deposited all of the minerals, so the pipes won't continue to rust. But, when you have air in there (from leaks or continually having to add water which will contain some disolved O2), rust continues, eventually destroying the pipe. Since rust is larger than elemental iron, when it flakes off, it exposes raw metal, and just keeps going while there is oxygen to allow the process.

You might have to disconnect that radiator, ream out the rust or replace what has failed, then, if it is still solid enough, re-install it.

Sounds like to me, if one has reached this condition, it is likely others are close and will do the same. No way to tell how much longer you'll have, but keep in mind, most new systems will probably use as little as 1/2 of the fuel yours currently does. Plus, there are often utility company rebates for updating. I got $1100 back for a new boiler and indirect storage tank from my gas company last year...
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
If there are no radiator traps (and that is fairly common also in residential steam systems) then the return pipe is plugged. There are no chemical products that will clear this out without eating through the pipe. There is a slim chance that only an elbow is plugged but more likely the pipe itself has rusted shut over the years. Unfortunatly when systems reach this stage you will begin having problems all over the house in the near future.
 

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
....Very few things are less efficient than steam.

Interesting I did not know that.

.....

Sounds like to me, if one has reached this condition, it is likely others are close and will do the same. No way to tell how much longer you'll have, but keep in mind, most new systems will probably use as little as 1/2 of the fuel yours currently does. Plus, there are often utility company rebates for updating. I got $1100 back for a new boiler and indirect storage tank from my gas company last year...

Both good points. With the price of fuel it will be very easy to justify replacement. Payoff may be a very short time. "Do the math", friend.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Undoubtably there will be some that will defend steam heat, but the fact is that you don't get any heat untill the water gets to 212 degrees.
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
If the pipes in the walls are rusted shut, then what is replacing the boiler going to do?

When you say replacement, you are talking about the pipes in the walls, right?

What kind of test can I do to determine if it is indeed the pipes that are rusted shut?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Unless you have a valve or thermostat in that radiator, I think you've already figured out...it's likely time. And, yes, it may be time to bite the bullet and repipe, cleanup or replace the whole thing. Some radiators can be used for hot water systems, or you could switch to baseboard heat, or consider radiant panels or radiant floor heat.
 

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
If the pipes in the walls are rusted shut, then what is replacing the boiler going to do?

When you say replacement, you are talking about the pipes in the walls, right?

What kind of test can I do to determine if it is indeed the pipes that are rusted shut?

You could probably convert a steam boiler to hot water but why bother? A new boiler will be much more efficient so will pay for itself rather quickly.

It seems that you will need to replace the pipes. You can very likely recondition the cast iron radiators though, although it would probably be cheaper to buy some new panels or baseboards. It depends more on style than anything else.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
If the pipes in the walls are rusted shut, then what is replacing the boiler going to do?

When you say replacement, you are talking about the pipes in the walls, right?

What kind of test can I do to determine if it is indeed the pipes that are rusted shut?

The radiator full of water is all the test you need.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
I know you don't like the thought of a new heating system and the associated cost, however how old is your boiler? If it's more than 30 years old it is doing you no favors at all. You already know the price of fuel and have probably projected this years bill. Doubt you were happy with your estimates, none of us are. Steam is a horribly inefficient way to heat. Before you get any heat at all the boiler must heat the water to 212. It takes a lot of energy to heat water to 212. Far more than heating it to 180. The boiler AFUE efficiency is also probably down in the 75% or less range also. New boilers are in the mid 80% range. If you are heating with oil I'll bet that oil tank is 30 years old and getting ready to start leaking also. It's a big initail cost but changing the system out to forced hot water will save you probably near 1/2 your current oil bill annually. Especially if you put in a very high efficiency unit with modulating reset controls. I've been in the heating business for 30 years now and believe me that old steam system will give no nothing but problems once the piping starts to go.
 

Southern Man

DIY Hillbilly
Messages
525
Reaction score
0
Points
0
Location
North Carolina
Not to mention the danger of getting burned on a steam heated radiator. I got a few of those from my childhood home.

Plus on most days when its not so cold outside a new system can a reduce the boiler temperature, increasing efficiency and making the house a more even temperature.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Steam has a lot of energy stored in it. It takes a fixed amount of heat to move from say 211 to 212 as liquid, but around 333x that energy to turn that same amount of water into steam. You get the idea. You have to move more hot water to warm the house than steam, but it is much easier to modulate. Unless you create a vacuum, you won't get steam until you heat it quite hot which also makes it more dangerous.
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
The boiler I would say is about 15 years old and is gas powered. I know that hot water is more efficient but I would have to run return pipes from each radiator to the boiler. I might do this in a few years. But for now I just want to pinpoint my problem. It's a rental apartment and they pay their own heat, so I'm not too concerned about efficiency, but I am still concerned and will probably convert in a couple more years when I could afford it.

If the radiator is filling up with water, Everyone hear agrees that the supply piping is clogged and is not allowing condesate to drain back to the boiler. Is that right? Is this the only possible scenario?

I heard someone mention that the automatic feed valve could be stuck open. This is not the case because then all the radiators would be full of water.

Then I guess I would have to replace the piping from that one radiator to the boiler.