Not sure what you used for a pressure reducing valve but it should have been something like a Watts S1156F or the Tack equivilant. These come factory set at 15 lbs which is about what you want for pressure. If you are getting a drastic increase in pressure when the circulator runs, you have the circulator mounted in the wrong place. It should be on the supply, pumping away from the tank (tward the zones) and past the expansion tank and fill valve.