Great forum. My basement was roughed in (unfortunately) only with drains for a sink and water closet, with a vent stubbed down from the first floor. I need to add a drain for a tub. Is it OK to set a side-inlet sanitary tee on the 3" riser for the water closet (just below where the closet flange will be), and run 2" to the P trap for the tub? I would plan to re-vent the 2" between the WC and tub drains, and also connect the vent to the sink. Or must I uncover the horizontal drain which runs to the water closet and tie into that? Thanks for any help.
 

Cal

In the Trades
Messages
228
Reaction score
0
Points
0
Location
Northern Virginia
Sounds like you have a good understanding of wastes & vents. If you can,it would be better to cut the 3" 90 off at the downstream side, Put in a 3" "side inlet" 90 (has a 2" cup in the side) Also called a side inlet closet bend.Bring your riser back up for the WC , pipe your lavy and shower off the 2" making sure to wet vent the group off the lavy. More work but worth the trouble in the long run. Good Luck !
 

woodyi

New Member
Messages
2
Reaction score
0
Points
0
Thanks for the reply Cal. I'll go ahead with the side inlet closet bend. FYI, the lav was previously run with 2" separately... I'm not sure where it ties in to the main. So I'm planning to use the side inlet from the closet bend for the tub only. I will tie the lav to the vent and plan to re-vent between the tub and WC just to be sure it's all vented adequately. Woody
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks