Further research has indicated that I do need to derate when using NM.
|
|
|
I want to put a subpanel in the garage. According to Table 310.15(B)(6), I would need #4 Copper for a 100amp subpanel. Is this table for individual conductors in conduit or can you use ROMEX® to feed the subpanel at 100amp? The reason I ask is I read that when using ROMEX® you had to derate the THHN in ROMEX® to the 60*C rating.
Thanks,
Mike
Last edited by Terry; 12-07-2011 at 10:08 AM.
Further research has indicated that I do need to derate when using NM.
Do just a bit more research and you will see that Table 310.16 must be used also
You are not "derating" anything. NM cable simply must use the 60 deg C column.
IF you did need to derate the cable you would do so from the actual insulation temperature column which is 90 deg C.