    Default Using ROMEX® to feed subpanel, do I have to derate from Table 310.15(B)(6)

    I want to put a subpanel in the garage. According to Table 310.15(B)(6), I would need #4 Copper for a 100amp subpanel. Is this table for individual conductors in conduit or can you use ROMEX® to feed the subpanel at 100amp? The reason I ask is I read that when using ROMEX® you had to derate the THHN in ROMEX® to the 60*C rating.

    Thanks,
    Mike
    Last edited by Terry; 12-07-2011 at 10:08 AM.

  2. #2

    Default

    Further research has indicated that I do need to derate when using NM.

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Do just a bit more research and you will see that Table 310.16 must be used also

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    You are not "derating" anything. NM cable simply must use the 60 deg C column.

    IF you did need to derate the cable you would do so from the actual insulation temperature column which is 90 deg C.

  5. #5
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by Mr_Magoo View Post
    I want to put a subpanel in the garage. According to Table 310.15(B)(6),

    Thanks,
    Mike

    As already mentioned, you cannot use table 310.15(B)(6).

Similar Threads

  1. ROMEX®/cable color changes
    By taz110 in forum Electrical Forum discussion & Blog
    Replies: 33
    Last Post: 09-08-2013, 10:28 AM
  2. ROMEX® to dryer outlet - insulated ground?
    By Plumbob in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 12-23-2009, 05:35 PM
  3. Adding Circuits using ROMEX® vs. AC cable
    By mrhoades in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 02-14-2009, 08:44 AM
  4. table saw question
    By shluffer in forum Remodel Forum & Blog
    Replies: 24
    Last Post: 05-23-2008, 07:58 AM
  5. Table Lamp
    By Fudog in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 01-01-2008, 06:24 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •