Gas line question

Users who are viewing this thread

goofy_american

New Member
Messages
6
Reaction score
0
Points
0
Good day,

I am installing two new Heat-n-glo fireplaces. I need to run gas lines to both locations.

Here in Mn, 1/2" flexible copper is allowable under code.

One fireplace is approximately 33 feet from the regulator and the other is approximately 40 feet.

Being that copper is so expensive, I was thinking about running a single copper gas line to the first fireplace and then putting in a T to run copper to the second fireplace.

We may run both fireplaces occasionally at the same time.

My question is will we have enough gas flowing through a single pipe and the T connector to feed both fireplaces or should I really run two 1/2" lines from the regulator?

The ceiling is open so it's not hard to do - I'm just trying to avoid having to pay an extra $75 for copper. I'd much rather do the flexible copper rather than black steel since this is a DIY job and I'd like to avoid having a lot of connections in the walls.

Thanks for any & all advice.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
My advice is that gas is not a DIYer project.
The plumber will know what to do!

It sure beats owning a vacant building lot with a smoldering pile of toothpicks on it, or, your family not getting up in the morning.:cool:
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Gotta go with Redwood on this. Gas piping is not really a good DIY project. You can screw up with water lines and all you have is a wet mess, but make a boo boo with gas, you can die. My guess would be that the plumber will use black iron pipe at least for the long runs then possibly transition to flex line to make the connections to the fireplaces although he might do it all with all iron pipe. Seriously, this is one job you should hire a professional to do.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
1/2" copper will not be large enough to service 1 appliance let alone 2. When insufficient gas volume is delivered to an appliance it will still operate, however the flame produced will not be as "hot" as it should. This can and does lead to excessive amounts of carbon monoxide produced. This piping should be sized correctly and installed by a licensed contractor.

Rule of thumb: GAS GOES BOOM!
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
In answer to your question, the total BTU's of the two appliances, and the length of the run, determine what size pipe is required. The National Fuel Gas Code book is where you find the charts to enter your btu and distance, and pull of pipe size.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
But Jimbo,
For a DIYer to join the NFPA and buy the book a plumber would be cheaper! LOL
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Actually, you don't have to be an NFPA member.( I am not....membership costs too much!) to buy the books. And the fuel gas code is not expensive.

I am following my usual practice that I will try to help a determined homeowner....rather than leave him to flounder around and then blow himself up, which with some help possibly we can avoid. And if he asks nice, myself or someone might just even look up the numbers for him!

I know that some take a hard line approach to gas. Such is life. Homeowners will do gas work, and Osama bin Barrack may be president. Like goes in in either case!
 

goofy_american

New Member
Messages
6
Reaction score
0
Points
0
Thanks for all the replies guys (and gals?),

I understand your concern and appreciate your thoughts.

The fireplace gas input is 1/2". The gas regulator output is 1/2". The furnace, water heater, gas clothes dryer and gas stove are all 1/2".

My plan is to buy 33 feet and 40 feet of 1/2" flexible copper - with no connections in between the regulator and the fireplace.

I will flare the ends onto the cables.

I plan on getting a permit so will have the gas line pressure tested.

Once the gas line is connected to the regulator and the fireplace, I will check the connections with a non-corrosive agent like soap suds to make absolutely sure there are no leaks.

I even have a gas detector and will plug it in to make sure there is absolutely no gas leaks.

Taking all these precautions, it doesn't seem like a big deal to me.
There will only be 2 ends of each gas line.

Am I missing anything? I don't feel like I'm being reckless...

Thanks again!
 

Wrex

Member
Messages
126
Reaction score
0
Points
16
Location
New Jersey
Jimbo's advice is spot on the BTU rating of the appliance or appliances and distance determines the gas pipe size.

The larger pipe reduces the pressure drop over long distances the pipe can then be reduced again with a reducing coupling to the proper size for your appliance.

With all the precautions you are taking including the pressure test you will be fine just make sure that you get the sizing right I can't stress this enough.
 
Last edited:

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
One more time. 1/2" copper is not large enough to carry the gas volume needed. Even though the regulator is 1/2" that does not mean the gas line should be 1/2"
If you're running 33' and you have other gas appliances you will need to run this line in black iron pipe.
 

goofy_american

New Member
Messages
6
Reaction score
0
Points
0
Both fireplaces are Heat & Glo.

The main floor living room fireplace (33 feet from regulator) is a SL-750TR.
BTU's is 16,900 to 24,300 BTU/Hour Input (NG).

The basement fireplace (40 feet from regulator) is a SL-750TRS.
BTU's is 20,200 to 30,800 BTU/Hour Input (NG).

Thanks again!
 

goofy_american

New Member
Messages
6
Reaction score
0
Points
0
More info from the manual -

Pressure requirements for both units:

Natural Gas:
Minimum Inlet Pressure - 5.0 inches w.c.
Maximum Inlet Gas Pressure - 14.0 inches w.c.
Manifold Pressure - 3.5 inches w.c.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
You can find the tables in the National Fuel Gas Code Handbook.
I would give you the correct information but I have a huge problem with assisting someone in doing their own gas piping. The appliances that you are planning to install have some very specific piping and valving requirements and must be properly installed or they are unsafe to operate. That you do not know, or even know where to find the proper sizing tables tells me that you are in no way qualified to do gas piping. Do yourself a favor and have either the gas company or a licensed professional do this job before someone gets hurt or killed.
 

goofy_american

New Member
Messages
6
Reaction score
0
Points
0
nhmaster, thank you for your concern but I respectfully disagree.
I am going to be installing Type L flexible copper gas lines with no connectors.

There will be two flared ends and the entire line will be pressure tested.

From the chart posted, I can see that Type L copper line at 1/2" nominal at a length of 40 feet will be approximately 41 MBH. One MBH is equivalent to 1000 BTU's per hour.

The larger fireplace only needs 30,800 BTU per hour.

This isn't rocket science. The city inspector wouldn't let me do it if it were so dangerous.

Care and caution will be used.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Type L copper can not be flared. Thanks for re-inforcing my point. No matter though, you will go right ahead and do what ever you want. Frankly I'm tired of trying to save the world. Enjoy yourself. Bring marshmellows.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Tell you what. You run on down to the cheepo deepo and grab a stick O type L copper. Its the one with the blue stripe down the side and says type L right on it. Then apply your flaring tool and see what you come up with.
Not one, but both of your DIY bibles are wrong. One is just wrong and the other is probably a typo. Type K is soft copper, suitable for flaring, not type L. But you are more than willing to argue the point with me and most likely every other plumber on this site. Why waste time though? you have it all figured out, now go on ahead and get to it.
 