External Outlet requirement

Users who are viewing this thread

chippie

New Member
Messages
1
Reaction score
0
Points
0
We've recently had a room addition to our existing home. Everything has passed inspection except for the new external outlet. The outlet is a GFCI receptacle. The problem is that the inspector said we must also have an AFC or GFC installed in the circuit breaker. When the electrician installed the AFC in the circuit breaker and a radio was plugged in the receptacle, the breaker tripped and cut off power. When the line is attached to a non GFC in the circuit breaker, the GFC outlet works fine.

My question is, if code requires both GFC circuit breaker and outlet, what could be a possible solution to the problem?

Thank you in advance for your help.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
We've recently had a room addition to our existing home. Everything has passed inspection except for the new external outlet. The outlet is a GFCI receptacle. The problem is that the inspector said we must also have an AFC or GFC installed in the circuit breaker. When the electrician installed the AFC in the circuit breaker and a radio was plugged in the receptacle, the breaker tripped and cut off power. When the line is attached to a non GFC in the circuit breaker, the GFC outlet works fine.

My question is, if code requires both GFC circuit breaker and outlet, what could be a possible solution to the problem?

Thank you in advance for your help.

I would ask for the EXACT code violation. :rolleyes: AFCI protection is NOT required for outdoor outlets, whether they are lighting or receptacles.
 

Brownizs

In the Trades
Messages
193
Reaction score
0
Points
0
Location
Springfield, IL
Easy fix, find a new inspector. Second fix, ask the first to provide the code reference, and what code the city goes by. Looking at one of the Inspector Forums, it amazes me how some of those guys stay in business, due to they are just like you and I, ask 100's of questions, and then still doubt what they see during the course of work that they are paid to make sure is correct.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
Is that outside outlet on its own circuit or does that circuit also provide power for things inside as well?
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
AFCI protection is NOT required for outdoor outlets, whether they are lighting or receptacles.

What if they are tapped from a bedroom circuit?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
It's not that it can't have AFCI protection, it doesn't require it for an outside outlet...
 