    I am in the process of remodeling my early 60's house here in Atlanta and have question that I can't seem to find an answer.

    My master and guest baths sit directly above my utility room which houses my fuse box (I am going to upgrade- just not quite there yet). The master and guest baths are split by a bathtub shower (doors on both sides of the tub- one set opens to the master, the other set to the guest bath) and I want to make the 2 completely seperate baths. I am going to stip everything down to the studs and start from scratch. Now my question, right now the end of the tub sits almost directly over the fuse box. When I spilt the bath in 2 I will have a bathtub that sits almost directly over the fuse box and a shower (stand up) that will be directly over the box. Is this an issue? I have asked a lot of experts and no one can give me a decisive answer. Anything would be appreciated.
    Shawn

  2. #2
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by Big Dawg View Post
    I am in the process of remodeling my early 60's house here in Atlanta and have question that I can't seem to find an answer.

    My master and guest baths sit directly above my utility room which houses my fuse box (I am going to upgrade- just not quite there yet). The master and guest baths are split by a bathtub shower (doors on both sides of the tub- one set opens to the master, the other set to the guest bath) and I want to make the 2 completely seperate baths. I am going to stip everything down to the studs and start from scratch. Now my question, right now the end of the tub sits almost directly over the fuse box. When I spilt the bath in 2 I will have a bathtub that sits almost directly over the fuse box and a shower (stand up) that will be directly over the box. Is this an issue? I have asked a lot of experts and no one can give me a decisive answer. Anything would be appreciated.
    Shawn
    So your bathrooms are located on the floor above a utility room? If so, then yeah, its okay, but no pipes can run over the top of the panel.

  3. #3
    DIY Junior Member
    Join Date
    Sep 2008
    Location
    Atlanta
    Posts
    4

    Default

    Yes - the bathrooms are on the floor above. There is no ceiling in the utility room so I can see everything (will make work easier). When you say the pipes cant run above- how far from the sides or out in front of the box do they need to be?

  4. #4
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Quote Originally Posted by Big Dawg View Post
    Yes - the bathrooms are on the floor above. There is no ceiling in the utility room so I can see everything (will make work easier). When you say the pipes cant run above- how far from the sides or out in front of the box do they need to be?
    Then can run right next to the panel, just not OVER the panel. but by code this only applies up to the structured ceiling, then you would need some type of protection installed if you did want to run over the top of the panel.

  5. #5
    DIY Junior Member
    Join Date
    Sep 2008
    Location
    Atlanta
    Posts
    4

    Default

    Thanks. You just made my day. Your knowledge is invaluable and I appreciate your help.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default Chris 75

    Re. your avatar. If you should not fall DOWN stairs, does that mean it is okay to fall UP stairs?