    I need to add some outlets in my unfinished portion of the basement and add a subpanel next to my main panel. Is PVC okay to use indoors a residential situation? I can bend pipe, but I'm slower at it and often its not the best looking.

    -rick

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    If it is for protection from damage then you must use Sch80. If it is simply for looks then Sch40 is fine.

  3. #3

    Default

    Hi, thanks. Its just for appearance. I know I could shoot a piece of PT to the wall and run the romex down the PT to an outlet at 4 feet but its not the look I want. I'll spend the $$$ and time for the PVC.
    -rick

  4. #4
    Code Enforcement codeone's Avatar
    Join Date
    Sep 2008
    Location
    North Carolina
    Posts
    160

    Wink

    The reason for using pipe down the wall is for physical protection. Not so much for looks. The 2008 NEC requires schedule 80 pvc for physical protection if your using PVC.

  5. #5
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    Quote Originally Posted by codeone View Post
    The 2008 NEC requires schedule 80 pvc for physical protection if your using PVC.
    Just a note. This is not new for 2008. It's been in the code a while.