water running when nothing is on

Users who are viewing this thread

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
I had new water heater installed last month along with a 2 gallon thermal expansion tank which something I didn't have before. The plumber said that the tank was required by code. Ever since the installation I've noticed that the water continues to run slowly at the meter sometimes for several minutes after the water is turned of at the fixture. Longer after heavy usage. This is something that wasn't happening before. I contacted the plumber, State water heater company and the water company none of them offered any helpful answers. I just replaced the the water pressure reducer valve because I had a leak at the pressure relief valve on the water heater. This stopped the leak but I still have the water continue to run at the meter after water usage. The only way I can get it to stop is if i shut off the valve above the expansion tank and water heater. Then, the water shuts off right away but as soon I open that valve the water continues to run. The expansion tank is a Wellsaver LPT-2 2 gallon tank and it is installed right above the water heater right after the shutoff valve. Can anybody tell what is going on here and is this something I should be concerned with? I can't find much information on the tank. Do they require regular maintenance? Is there anyway to check if it working properly?

thanks
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
That is a strange one! I can't answer why the water continues to run after everything is off, but I can answer a bit about the expansion tank question. Let me start with a question. Did you use a pressure gauge and match the pressure regulator valve pressure to the expansion tank? They should be equal. And, just so we are using the same language to describe things, what you are calling the pressure reducer is usually referred to as a pressure regulator or PRV, and what you are calling the pressure relief valve is usually called the temperature/pressure valve or just T/P. You are correctly describing their functions, but there could be some confusion. The expansion tank is installed between the PRV and the water heater in the cold water supply. The tank has a rubber bladder that, just like everything else will fail. You will know it failed when the T/P valve trips and leaks water. There isn't much maintenance to do, just periodically check the pressure. It should stay where you have it, so if it changes, that may be a sign it is beginning to fail. Wish I could give some assistance on the other problem, but probably some of the pros that hang around the forum will chime in.
 

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
expanstion tank

Thank you for your prompt reply. I'm fairly certain that the plumber did not check the pressure in the tank or the water pressure to see if they matched. I don't own a water pressure guage so I can't check that. I just had new prv installed and it is factory preset to 50psi. Do I check the tank with a regular tire guage to see if it matches 50psi? Thanks in advance.
 

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
expansion tank

Just checked expansion tank pressure. I is at 54psi so I'm guessing that's fairly close to the factory preset 50psi on the PRV.
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
It sounds like as the flow of the water reduces so does the pressure going through the pressure reducing valve. It will reduce untill it reaches the pressure setting of the valve. I am going to guess that the water is flowing through your PRV at a much slower rate when it is close to its pressure setting than when the pressure differences are greater as they are while you are using water.

It does eventualy stop...yes?

It is how your PRV is operating at low flow.
 

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
expansion tank

Yes, it stops. How do I charge the tank to the correct pressure? Do I need to take somewhere to get it done or can I just use bicycle pump?
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Why do you want to change the tank pressure...it has nothing to do with what I just explained. Your PRV s the valve installed near where the water enters the house.

It controls the pressure on the house side of it.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
The pressure on the tank bladder will read its set point or the water pressure as long as the system is under pressure.
 

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
expansion tank

I was told by State water heater that the air pressure in the tank should match the pressure coming into the house. I checked it and it is below the 50psi preset on the PRV.
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
You need a pressure gauge to check the water pressure setting first. While the pressure setting should be 50 from the factory I have found that they are many times way off.

You also don't know what the plumber may have done.

Tanks are preset at 40 PSI. You need to call the plumber back and have him charge / check the tank if it is off.

Hack plumbers will many times just install the tank without setting the pressure to match the house pressure...I like my tanks to be 1-2#s lower than the house pressure.
 
Last edited:

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Never guess or assume what the pressure is in anything. A basic gauge can be purchased in any hardware store or plumbing supply for under $15. If, and I stress IF, the pressure in the expansion tank needs to be increased, Watts advises a bicycle pump. The actual volume of air needed is quite small so it would be easy to rupture the tank's bladder using an air compressor.
 

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
expansion tank

You were right about hack plumbers. He just put the tank in without checking the the water pressure coming into the house or the pressure in the tank. You would think a master plumber who installs water heaters for a living would have taken the time to do this. Anyway, I've pretty much had it with this guy after calling him back for one thing or another since the tank was installed so I decided to do it myself. I went to Home Depot and and picked up a water pressure guage for 10 bucks and a hand pump for 9 bucks. I checked the pressure at the hose bib and it was off the 50psi preset on the PRV so I tweaked it a little until it was at 50psi. Then, I shut down the water and drained the water heater a little to relieve the pressure. I removed the expansion tank which was installed directly above the water heater blower control box which I'm not to happy about. In his defense there wasn't much of an option this was the only exposed pipe in the finished basement. But, he could have angled it out away from the blower. I guess I will have to get some kind of angled adapter to remedy that situation if possible. Luckily the pump I bought was pretty sturdy, a Husky, so I was able to pump the tank up to 50psi. (this was not easy, it took some pretty hard pumping to get it up to that pressure....imagine pumping up a truck tire with bicycle pump and you'll get an idea what I mean) Anyhow, I put the tank back onto the cold water inlet to the water heater which has the tank in a horizontal orientation, hopefully this it ok positioning. I turned the water and water heater back on and voilla, no more running water after water is turned off.

Thanks for all your posts and if you can think of anything else to add or ask, please do.
 

crazebstrd

New Member
Messages
13
Reaction score
0
Points
0
expansion tank

Since the tank is installed horizontally, do I need to support it to take pressure off the fitting? If so, how is this accomplished. I received no instructions with the tanks since it was installed by the plumbing contractor and can't seem to find any information about them online. The tank is a Wellsaver LET-2, 2 gallon expansion tank, The water heater is a State Select 40 gallon gas powervent model. Any info would be greatly appreciated. Thanks again.
 

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
Water Heater

Go Pick Up Some Plumbers Tape And Drywall Screws Take 2 Wraps
Around Tank And Anchor With Screws To Over Head Beams Or Anything Above That Will Support Weight Because You Are Right
If That Bladder Fails The Tank Will Fill With Water And Break At The Fitting
 

Winslow

Plumber
Messages
445
Reaction score
0
Points
0
Location
Hawaii
Just checked expansion tank pressure. I is at 54psi so I'm guessing that's fairly close to the factory preset 50psi on the PRV.


You need to verify system presure with a gauge on a hose bibb. Don't assume it is 50 lbs based on a stated preset rating. The PRV adjusts pressure relative to the incoming pressure, therefore any preset pressure rating would be relative to incoming pressure. For instance it may be preset for 50 lbs based on incoming pressure of 80 lbs. If incoming pressure is actually 100 lbs then it would reduce it to 70 lbs.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
The PRV adjusts pressure relative to the incoming pressure, therefore any preset pressure rating would be relative to incoming pressure. For instance it may be preset for 50 lbs based on incoming pressure of 80 lbs. If incoming pressure is actually 100 lbs then it would reduce it to 70 lbs.

Ummm not quite...
It functions as a regulator and the pressure would be at the set point unless the supplied pressure is lower than the set point.
 

hltibbs

New Member
Messages
1
Reaction score
0
Points
0
Location
Ohio
Low water outlet after installing LET-2 expansion tank

I just installed a LET-2 on a 50 gal electric heater yesterday and now the tenants are complaining of very low water output at the faucets. The inlet and tank pressure are within a few pounds of each other (50 +/-).

What would cause this low hot water output and how do I fix it?
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
It could be a number of things.
The valve you shut the water off with may have broken and not opened all the way back up.

Or the aerators on the faucet may have plugged with debris dislodged while you were working on the system.
 